Solis PV inverter and AC coupling

@Phil_Gavin

I recently installed a new Solis 3 Kw PV inverter coupled to the AC output of a Victron Multi. The Multi is ramping up the frequency when the battery is full, as set up in the "assistant". The Solis does not respond to frequency rise, and continues to supply power and over charging the batteries. I contacted the seller, and Solis tech help, to ask what settings I should use to make it happen. They tell me the version of the Solis made for the UK market does not support the frequency derate option. On this Solis home screen it says LimByFreq which I took to mean what it sounds like. My quetion for you is : Do you think this is right ? If you are UK based what settings did you use to achieve the power control ?

AC PV Coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Paul B avatar image
Paul B answered ·

This is just a suggestion

as you have not mentioned the freq setting you have set, try increasing the freq setting to say 55hz in the assistant as I am pretty sure that all grid tie inverters have to shut down by a frequency shift, but some will also de-rate at different settings

NOTE the Multi plus can only raise the frequency if the mains input has failed.

secondly if they don't and you are stuck with them then you could install some contractors in the incoming grid tie inverter lines that are triggered on/off by setting up a assistant in the multiplus to turn the contractors off if battery voltage went above a set figure and back on again at a lower figure,

For that matter you could conect the grid tie inverters to ac2 out and use the assistant to turn this internal relay on and off based on a DC voltage trigger

Just some ideas hope they help in your setup


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Robert Bazalgette avatar image
Robert Bazalgette answered ·

Hi Paul, Thanks for responding to this. I tagged @Phil_Gavin because he wrote that he has used a Solis inverter for frequency controlled AC coupling. The Solis will switch off if it sees out of range frequency, but I want to use the frequency de-rate function to optimise power from the PV inveter. That means de-rating the output gradually in respose to the state of charge of the batteries, rather then just cutting out.

It is frustrating because the Solis information shows a graph of linear power reduction from 100 to 0 % as the frequency rises from 51 - 52 Hz, which is exactly what I need it to do. When I contacted Solis they say this is only available on US models, which seems wierd.

On the Victron Multi, when you load the assistant for frequency de-rate, it tells you that this will not work when you are coupled to a grid on the AC input. That is fine, this set up is entirely off grid.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Phil Gavin avatar image Phil Gavin commented ·

I am in a different country to this set up at the moment, so I can't check on further specifics.

As far as I remember, this setting may be related to the country chosen in the settings. The other thing I understand is that the various certifications this inverter has (such as VDE4105 and others) mean it is certified to behave with a gradual frequency derating response in accordance with the laws of different countries.

I bought this inverter second-hand from the UK , the settings were pre-configured and it just worked without any settings changes. I have it in an off-grid scenario as well, so I didn't try to fix what wasn't broke, as I am also 230V 50hz.

I confirmed this functionality before I bought the unit, so I believe it is also described in the Solis documentation.

Sorry, I can't be of more help at present.

0 Likes 0 ·
Paul B avatar image Paul B commented ·

RE this - On the Victron Multi, when you load the assistant for frequency de-rate, it tells you that this will not work when you are coupled to a grid on the AC input. That is fine, this set up is entirely off grid.


Thats correct But what Victron mean by this is that freq change CANT happen while GRID power is connected, so in all other cases it does happen if setup correctly.

0 Likes 0 ·
yann avatar image
yann answered ·

in the solis network standart setting, you need to choose the "gen50" (or gen60 for 60hz) setting, then you got the frequency derating from 50 (100%) to 54hz (0%)

it works nicely


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mikhail-petukhov avatar image
mikhail-petukhov answered ·

@Yann could you please share Solis model and firmware version? Probably they support "gen50" feature for new models only or from a specific firmware version.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

yann avatar image
yann answered ·

@Mikhail Petukhov the model I just tested is a S5-GR1P2.5K-M (2.5kW, 1mppt) but I have no idea wich firmware is running inside, and I can't see it right now (my customer is gone for some weeks)

I read somewhere the S4 models (previous generation) already have the "gen50" mode.

On the S5 I have, there is also a "manual setting" that let you define everything as you want, but there are tons of parameters wich is not clear what they are for. Nothing in the user manual about them.