The idea would be to transfer the energy to 230V. Like a ToGrid conection.
Hi @Ship Tyr
You could plug in another boat on your inverter output.
If you connect it to AC output-2 and program that output to only turn on above x% SOC, you can automatically stop feeding when the battery is below x%
@Daniël Boekel (Victron Energy Staff) But, the output2 only works if I am connected to the shore power. or can I activate it in island operation?
Yes you can program it to you need.
some hints on how you can do that:
https://www.victronenergy.com/live/assistants:ignore_ac_input_using_the_generator_assistant
https://www.victronenergy.com/live/assistants:overview_of_available_assistants