System Design:
I have 3 Lion Energy UT1300 LiFePO4 105Ah batteries. They each have an internal BMS and are the 'drop in' replacements for deep cycle Lead Acid batteries. They are rated for maximum 100A charge / 150A discharge each and are connected in parallel using 4/0 AWG cables. On the negative terminal I have 12" 4 AWG cable to a BMV 500A shunt and then 24" 4 AWG cable to a Lynx Shunt. On the positive side I have 24" 4 AWG between the battery bank and a BlueSea m6000 disconnect switch, then 12" 4 AWG from the switch to the Lynx Shunt. The Lynx Shunt is connected to a Lynx Distributor. Then I have a MultiPlus 12/3000/120 connected to the Lynx Distributor via (2) 36" 4 AWG cables and a 400A Mega Fuse. The Lynx Shunt has a 800A CNN fuse. The MultiPlus has the voltage sense connected using a fused 20 AWG wire to the battery terminals. I know the 4 AWG wiring is not ideal, I will replace with larger wire in my final installation, I don't know if it is the source of my issue. Here is a crude wiring diagram
Issue:
I can discharge the batteries fine, the problem occurs during charging. When the MultiPlus transitions from Bulk to Absorption problems occur. They range from interrupted charging (Absorption voltage set to 13.9 - 14.1) to complete shutdown of the MultiPlus (Absorption voltage set to 14.4 - 14.6).
Here is a picture of the PV during charging showing the transition between bulk and absorption. The absorption voltage is set to 13.9, the unit seems to stop charging after the transition to absorption.
Here is the picture of PV when the MultiPlus absorption voltage is set to 14.4 Volts. The drops during the absorption mode represent when the MultiPlus shuts down and then resets itself. During the shutdown all lights are off and AC1 is off. NOTE: The voltage spikes seem to follow the current peaks. The MultiPlus will continue this interrupt cycle indefinitely until I intervene.
Question:
1. Has anyone else seen this behavior?
2. Could this be caused by the BMS shutting down during charging?
3. Could this be caused by using 4 AWG cable?
4. Could the MultiPlus design be causing the voltage spike?
5. What would a normal PV chart look like during absorption mode? I have read absorption mode is a constant voltage with reducing current until charging is complete.
Thanks in advance for any help.