Can I make AC OUT 2 active on inverting (Quatro)

I would like to have the possibility to switch on AC OUT 2 under specific circumstances.

Battery's full, normal alternator is on for a long time etc

I see similar questitions, but I cannot find how to setup Assistanst or VS for this.

Harold

ac out 2
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

What you need is the "programmable relay" assistant. And select the AC OUT 2 relay.

Just download, install and start VE.config (VE Configuration tools for VE.Bus Products).
Then click on "Port selection" -> "Fake target with full options" -> select what you need -> OK -> Assistants -> read -> "Do this for me" -> Add assistant -> Relay -> programmable relay -> Start assistant .
There you can see what options you have.
Note that you need one assistant to activate the relay and one to deactivate it.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

harold avatar image
harold answered ·

Thanks!

This (with the 2 assistants) will be extra to the standard functionallity (AC in --> AC Out 1+2)?

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

No, if you use assistants to activate/deactivate AC OUT 2 the default behavior of AC OUT 2 is disabled.
If you want this you have to use an additional assistant.

0 Likes 0 ·
harold avatar image harold Matthias Lange - DE ♦ commented ·

Thanks again for your quick reply!

This is what I made:

(AC2IN = shore power ; AC1IN = generator)

(AC2OUT = heater etc)

0 Likes 0 ·