Quite special setup here, I know.
An MPPT 250/100 will charge 19.2 kWh of lifepo4 batteries and a Multiplus II will give me AC.
To charge event on the cloudiest days the solar field is greatly oversized (18kW) and the same PV is used directly to power other loads (water or space heaters in DC straight from the panels). The idea is to connect/disconnect strings in real time to the MPPT as required in order to ensure that the Isc on the MPPT is always low enough and to let the excess PV go to the heaters without affecting MTTP or any component of the electric chain.
The swapping will be performed by an external device driving one relay per string (on the positive pole). The logic will depend on SOC, current delivered by the MPPT and potential errors. In a very simplified version it could behave like this:
- Battery not full and charging current < 50A for more than 30 seconds: connect one more string to the MPPT and wait 30 seconds for MPPT or anything else to stabilize (if it's the first string being connected enable the MPPT also).
- Battery not full and charging current >90A: immediately disconnect one string and move it to the water heaters, wait 3 seconds before testing again.
- Battery full or MPPT not charging: disable MPPT and move all strings to the heaters.
Each string will deliver 1500W maximum (aka 30A to 35A on a 48V battery) so it's important, to ensure stability, that the high threshold and the low threshold are more than 35A apart (in this example 40A has been chosen).
Now the 1 million dollar question: will the MPPT 250/100 or the PV be annoyed by said circustances?
I guess that a selected power point will get disturbed when swapping panels but it should return to the MPP at some point, my concern is if these disturbs could damage the MPPT or trigger a fault. It could look to the MPPT like a very fast cloud covering or uncovering the sun... veeery fast!
I'm not interested in optimizing the speed of charge. The MPPT of course won't be delivering its maximum current at any time in this setup.
Thanks