Can or I cant to connect two MPPT in parallel mode in the PV Side?

We need to conect two Smart MPPT 150/100 in parallel mode, both sides (PV and Battery)

There is not information about it, please coud You help me.

In advance, thanks so much


Jorge G

smart solar set-up help
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

On the battery side it is no problem but on the PV side.
Both charge controllers try to find the MPP and this ist not working.

Why do you (think you) "need" to do that?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jorge-gonzalez avatar image
jorge-gonzalez answered ·

Please could You explain me why it could be a problem?, is it destructive? If the problem is MPP, because each controller will try to get their best performance. even that it would work, perhaps the controller doesnt share the load but.. must work.

Why do you (think you) "need" to do that?, because we have a big PV array and i have not option to split it in two arrays.

Could Ypu tell me if we can configure the controllers to work like PWM and not in MPPT mode?

The load current is around 1000W in 48 Volts, so we need to recharge with at less 120Amp.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image
Justin Cook answered ·

@JORGE GONZALEZ, it is not possible to connect two separate MPPT controllers to the same PV array. You can size up to a larger controller as appropriate to your array size, or you can split your array into a manageable size for the two 150/100s that you reference to handle, but these are the only two options.

It is also not possible to configure an MPPT controller to be a PWM controller; these are two vastly different types of SCC that behave in entirely different ways.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jorge-gonzalez avatar image
jorge-gonzalez answered ·

Really I understood your answer, but in this moment i have not option to get a larger controller.

Please your advice, It could be destructive? or will just work just one of them?

12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image Matthias Lange - DE ♦ commented ·

I don't think it is destructive but you will get much less power.

0 Likes 0 ·
jorge-gonzalez avatar image jorge-gonzalez Matthias Lange - DE ♦ commented ·

Thanks so much for your reply,

Really in this moment I cant split the PV array, but soon I will doit. Just I need to connect it in a parallel mode for few weeks.

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ jorge-gonzalez commented ·

@JORGE GONZALEZ

Just to be sure: how are the panels wired now? what voltage / current do you have now and what will you have after splitting?


0 Likes 0 ·
jorge-gonzalez avatar image jorge-gonzalez Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Hello, thanks for Your support:

now we have:

36 solar panel, 9 array of 4 panel in serie.

the solar panel VOC is 37,2V x 4= 148,8V

We have each panel in 250W .. 36*250W= 9000W

permanent load current=25Amp

So we need to recharge our 1000AH with a DOD of 50% with more less 150 amp.

We need for a few time tohave both controllers in parallel mode (PV Side), please could You give me your Tips or advices???

at the end, I uderstood that in the victron controller, if the current is less than 2 amp, it will limit the current avoiding to overchage the battery...but this is not the case. (because our currente is higher than 20 amp)