15.t volts going to battery from charge controller

Hi. So when my mppt 75/15 is sending 15.5 volts to my battery. Which as now happened on 3 occasions. Why hasn't 19amp fuse blown on the cable going to the battery. I can only think the last time it happened. The chatge controller was in the garage. Once it warmed up it worked as normal and went to float after a while. And didn't go above 14.2 on volt meter

fuses
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Steve avatar image Steve commented ·

In my motorhome a alarm goes off for overcharging when it giving out 15.5v

0 Likes 0 ·
3 Answers
Steve avatar image
Steve answered ·

Sorry 10amp

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Steve avatar image
Steve answered ·

Sorry should read 10amp fuse

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image
Justin Cook answered ·

Hi @Steve, a couple of things: First, the fuse between the 75/15 controller and battery should generally be a 25A fuse, since the controller could put out up to 15A and you don't want your fuse blowing if the controller reaches its full potential. This depends on the wire gauge and length you have running from your controller to your batteries, however, so maybe you've sized the 10A fuse according to your wire gauge - in which case, leave it as it is.

Second, the fuse you have didn't blow because your high voltage does not equal high current; the fuse is a 10A fuse, which means it will blow if more than 10A flows through it for a certain period of time, but the fuse can probably handle 32-48v or more. A little 15v running through it isn't something the fuse is going to notice.

And, finally, you're most likely seeing the voltage that you are as a result of the controller compensating for low temperatures, which so long as you're charging a lead battery, is perfectly appropriate. Pb batteries require higher voltage to charge at low temperatures because their internal resistance is higher; then as the battery/controller warm up, the voltage will drop off. This behavior is addressed in section 1.6 of the user manual.


4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Steve avatar image Steve commented ·

Hi. Thanks for reply. Its a gel leisure battery. So is it not a problem that it sending over15v to the battery. I thought that that was overcharging the battery. The ad I guess is a fused lead for this purpose maybe around 18inches long

0 Likes 0 ·
Steve avatar image Steve commented ·

It came with 15amp fuse but after seeing over 15v going to battery. I put 10amp in hoping fuse would blow before overcharging

0 Likes 0 ·