dyju711 avatar image
dyju711 asked

Wind turbine inverter as AC In to the Multiplus?

Hi Guys, I'm planning my off-grid system and I need some help with the design.

My initial plan is to use Mulitplus II GX/MultiGrid with DC coupled PV connected to the BYD battery pack. The issue at this stage is the optimal connection of the wind turbine (3 phase generator).

Inverter recommended for this turbine can operate in both on-grid and off-grid installations. In on-grid mode it would be connected to AC out of the Mulitplus. If I'm not wrong surplus energy can be used to charge the battery but without any control of the Victron or BYD BMU.

Off-grid model can be connected to the batteries and work without the grid but the communication with BMU/BMS isn't supported.


Do you think that it's possible to use output of the wind inverter as an input to the Multiplus (or as genset for MultiGrid)?

This is a schematic for the off-grid, 'connection point to the electricity grid' will be the Multi.

Both Multi and PS100 will be connected to the same battery pack, but charging/discharging will be disabled in PS100. This should allow Multi to use power generated from wind to charge the batteries in line with BMU communication. If I'm not wrong it will also resolve the problem with overcharging the batteries.


What's your thoughts about this approach?

Hydro and Wind Power
wind-off-grid.png (60.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Dyju711

You'll have to treat the wind inverter the same as a PV inverter, so connect it to the output (or if you'd have a grid connection you could use it on the input also)

Please check if the inverter supports frequency shift control and take the 1:1 rule seriously.

https://www.victronenergy.com/live/ac_coupling:start

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dyju711 avatar image dyju711 commented ·

Thanks @Daniël Boekel (Victron Energy Staff) for your response.

Unfortunately the wind inverter does not support frequency shift. It requires connection to dump load resistors but I'm not sure if this will be enough to not overcharge the batteries.

Based on PS100 manual it seems like it can create 230V 50Hz output after connecting to the batteries. I was hopping that Multi/MultiGrid will be able to accept it as a "normal" grid and operate in ESS mode. Wouldn't it work that way?

-1 Like -1 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ dyju711 commented ·

Hi @Dyju711

after reading a bit of the manual:

https://www.twerd.pl/images/pdf/ps100-user-manual-en.pdf

it seems that if you have the version with a battery, it can create a local grid. please note: this device needs a 96 volt battery, and that battery is -not- isolated from the 230 VAC the unit puts out.

I would not use the device with a battery, but as an 'on grid' installation. It -has- to support frequency shifting, otherwise it cannot work.

0 Likes 0 ·