Jon S avatar image
Jon S asked

Cyrix Li ct between Balmar 220A alternators and 614 external regulator.

@Daniël Boekel (Victron Energy Staff)


Hi Daniel,

Per your comment on my previous thread I am writing about 2 issues I am having. They are different so I will put them in 2 posts.


I have wired in a Cyrix Li-Ct between my house and start battery per this diagram:

If I attach the voltage sense to the Lithium batteries the voltage rises to 18v. If I attach the voltage sense to the start battery voltage is correct but I only see about 108 amps coming out of the alternator.


Any ideas?


Jon



Cyrix Battery Combiner
1584467230912.png (389.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Jon S

I don't follow your text

What voltage sense? of what device?

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jon S avatar image Jon S commented ·

@Daniël Boekel (Victron Energy Staff)


Sorry about that, it was horribly worded.


There is a Balmar 614 external regulator connected to the Balmar 220 amp alternators. I was referring to the voltage sense between the 614 and either the start battery or the lithium.

When connecting the voltage sense wire from the Balmar 614 direct to the start battery the alternator doesnt rise above 108 amps. When the 614 voltage sense is connected to the lithium's voltage climes to 18v. I shut it down fast so dont know what amps it is pushing.


Does this help?


Thanks,

Jon

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ Jon S commented ·

@Jon S

of course the alternator voltage sense has to be connected to the battery it is always connected to, if it senses the lithium battery while it is not connected to it, it will try to increase the voltage.


I -really- advice you to hire a capable installer for your system.

0 Likes 0 ·
Jon S avatar image Jon S Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

@Daniël Boekel (Victron Energy Staff)

As I stated before, I cannot find a reliable certified Victron engineer in St. Martin. I hired one to do the install and paid a shit ton of money for it. I hired another to review and his recommendations were worse. So now what do I do if you will not help me? I am technical and I am working with an electrician who was a Electrical Engineer.

Maybe its still not clear what was tested. Of course the voltage sense MUST be connected. It was never tested un-connected.

Test 1 - configured per the Cyrix Li-Ct diagram in previous post.

  • Connect voltage sense from the 614 to the start battery (which is AGM).
  • Connect amp meter to ground cable coming off alt.
  • Connect volt meter to start battery
  • Start engine
  • Review readings: 108 amps Volts 14.2
  • Stop engine.


Test 2 - This was recommended by a Victron certified installer (who left it like this and melted my start battery. I like my chances on my own).

  • some config as the Cyrix Li- ct diagram
  • Connect voltage sense from the 614 to Victron Lithiums.
  • Connect amp meter to ground cable coming off alt.
  • Connect volt meter to start battery
  • Start engine
  • Review readings: Volts 18 amps - didnt look, shut down due to 18V
  • Stop engine.
0 Likes 0 ·
Show more comments
gbarnaud avatar image
gbarnaud answered ·

Hi @Jon S, @Daniël Boekel (Victron Energy Staff)

I'm very interested in this topic as a customer is currently planning about the same configuration.

How many Ah lithium batteries are we talking about ?

By the way we decided to dedicate all power of the alternators to the house battery and charge the engine batt through a DC-DC 12V/30A charger.

We will stop the alternator charging by interrupting the ignition of the Balmar external regulator directly from the Charge Disconnect

I'm afraid the mix between the relatively high voltage of the fully charged engine batt and the not so low voltage of the Lithium batt at 70% explain why the alternator are not charging more. Even if 108A is not ridiculous, be honnest.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Art Hebert avatar image
Art Hebert answered ·

Hi Jon,

I am new to the forum... are you using any fuses in the wiring from battery to battery?
thanks

Art

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jon S avatar image Jon S commented ·

Hi Art,

The alternator side is fused per the drawing. That drawing does not cover the detailed house diagram. All house batteries are fused to the positive bus bar. The positive bus bar is fused to the electrical panels.

Jon



0 Likes 0 ·