Ignoring AC In using generator start/stop functio

Hey!
I have an issue.
the set is:

2 phase system with 2 multi 3000Va 48V Venus Gx, Blue Solar MPPT and Lead-Carbon batteries.

I am using the start/stop Generator Function to ignore AC In.

System should be disconnected from AC In, until the consumption hit maximum which can solar and batteries provide or until the multies overload or until the batteries fall down to certain soc.

I had set the parameters for overload, battery current, ac load and SOC and it works well until the system needs the grid, then it just kicks in and whole system runs on the grid even when the batteries could provide like 70% of load, it still runs only on grid.

I am using ESS so, point is, why the system don’t skip to the hybrid function? And is there any way to solve this ?

Ps: iam using the remote console seating for generator

ESSVRMGeneratorgrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Stanislav Vávra avatar image Stanislav Vávra commented ·

Thank you! I’ll try!

0 Likes 0 ·
Stanislav Vávra avatar image Stanislav Vávra commented ·

Thnx a lot! I’am using the aux 2 and it is working well now!