question

lief ryan avatar image
lief ryan asked

multiplus relay specs

i would like to confirm the multiplus 48/3000/35-50/230/ relay specs, i found a small note in the manual

(Programmable relay which can be set for general alarm, DC undervoltage or genset start/stop function
AC rating: 230 V/4 A
DC rating: 4 A up to 35 VDC and 1 A upto 60 VDC)

would i be correct in thinking that it would be ok run 230v through the relay for switching a contactor coil??


Thanks in advance.

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Rob Duthie avatar image
Rob Duthie answered ·

Hi

Depending on what version of Mulitplus you have you can't apply 230vac to the relay coil you have to use a interposing relay to do that. As below.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.