question

mauromartini avatar image
mauromartini asked

PV Throttling

Hello community,


I need some help please!


I have just installed my system:

1 x Multiplus 48/5000

1 x SmartSolar MPPT 15/70-TR

1 x Venus GX

1 x PylonTech US2000B 2.4kw

12 x 350w Canadian Solar


ESS is installed in 'Keep Batteries Charged'

DVCC -ON


My PV is peaking out at about 3350W. It seems that something is throttling the system.
I have followed the setup recommendation for the Victron/Pylontech setup.

System has been running for 2 days. When I first set up it would not work on ESS 'Optimised without Battery Life'. PV was on and then off, on and then off. I then setup as 'Keep Batteries Charged' and PV worked fine. End of the day, still on 'Keep Batteries Charged' the system went crazy again with PV on, off, on off, on off. I looked closer and it seems liked the 'State' on the MPPT was ESS/Fault.


I then reset as much as I could and everything started working again today. My PV is still peaking out at about 3350W.


Surely I should be getting at least 3800w out of the max 4200w? Is there anything I am missing?


Does this have anything to do with the jumpers on the underside of the MPPT? (untouched out of the box)


Unloaded my voltage is 130v on both strings of PV. Loaded it drops between 94v and 107v


Any help will be much appreciated.




MPPT Controllerssolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

I think you problem is that you have only one US2000B module.
A single module can be charged/discharged with 25A (continuous - 100A max for 1 minute).

So the BMS is limiting your PV power.
For your setup you should use 4 modules as it is recommended in the guide(you mentioned you followed!?):
https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·

This what I posited too, but I cannot explain the 3300W?

0 Likes 0 ·
mauromartini avatar image mauromartini commented ·

That’s the obvious answer. However it does not make sense. I am getting more that 25A but less than 30A from the PV. Also - once the battery is full why would the output from the PV matter as it is going directly to AC and grid?


I did certainly follow the setup instructions but as you pointed out I am short a few batteries (cost)

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ mauromartini commented ·

PV current ≠ battery current (MPPT output)

Do you have a screenshot of the MPPT output voltage/current at the same timestamp?

@warwick I think at the time you see at the screenshot there was a (big) load running at the AC OUT of the MultiPlus.
So all the available PV power goes straight into the Multi and the loads.

0 Likes 0 ·
Warwick Bruce Chapman avatar image Warwick Bruce Chapman Matthias Lange - DE ♦ commented ·

Feed in enabled.

0 Likes 0 ·
mauromartini avatar image mauromartini Matthias Lange - DE ♦ commented ·

Is this what you need? @M.Lange?

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ mauromartini commented ·

There should be a graph for "Solar charger battery voltage and current" and "AC output power".

0 Likes 0 ·
mauromartini avatar image mauromartini Matthias Lange - DE ♦ commented ·

@M.Lange Here you go. The Solar charger battery voltage and current was not selected so I could not see it. I see now it is pushing 65A. Will it not get to the full 70?

Just looking again: 65a x 52v= 3380w which is correct!


On MPPT when you select LifePo4 battery (no lithium option) the default is about 56v (from memory). But I have had to set the MPPT to 52v for the lithium battery.


Can I set the MPPT to 56 and will the BMS on ESS ignore this for battery charging?

Just trying to get as much out of my system as possible.


<span style="font-size: 14px;">I need the 52v to charge the battery. Should I have gone one size up in MPPT?</span>

<a rel="user" href="/users/1050/warwick.html">@warwick</a> FYI





0 Likes 0 ·
Warwick Bruce Chapman avatar image Warwick Bruce Chapman mauromartini commented ·

No.

The MPPT is rated for up to 50A short circuit current ie. on the solar side of the MPPT rather than the battery side.

So, if you're getting about 35A and around 100V then that's about 3500W yield.

8411-pv.png

0 Likes 0 ·
pv.png (90.5 KiB)
danepb avatar image
danepb answered ·

I have seen this before.

If you set your ESS SOC to 95%, see if that changes anything. I have noticed with a pylon if the SOC is set to 100%, the MPPT does throttle the unit, even when feed in excess power is enabled.


This is due to the battery voltage and the need of +-0.3V over the absorption voltage to feed back the excess power.


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mauromartini avatar image mauromartini commented ·

Ok thanks @DanePB. Would that mean I need to rather use the ESS Optimized (without battery life)


Little new to this.

0 Likes 0 ·
mauromartini avatar image mauromartini mauromartini commented ·

If so it did not help.

0 Likes 0 ·
danepb avatar image
danepb answered ·

I use the ESS Optimized (with battery life).


Give it a try


4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mauromartini avatar image mauromartini commented ·

@DanePB This works and I quickly got up to 3700w (slightly cloudy day) but as soon as Battery Life kicks in it drops down to about 60w.


So I retried it without battery life and set the SOC to 95% (think I forgot to 1st time) and seems to be working now!


It seems to be constantly charging and discharging the battery (top 5%) is that going to damage the battery?


Thank you very much


*Update: seems that it is when ESS #1 is active that the PV drops right down.

Another thing I tried is to disable the DVCC while on keep batteries charged. Is there any implication to not use the DVCC?


@warwick

0 Likes 0 ·
Warwick Bruce Chapman avatar image Warwick Bruce Chapman mauromartini commented ·

DVCC is compulsory with ESS and Pylontech.

0 Likes 0 ·
mauromartini avatar image mauromartini Warwick Bruce Chapman commented ·

Yes correct. Compulsory according to the manual. Reading the manual is not the problem. I need to get max yield or my spend on solar is partly wasted


Question still stands - what is the implication (other than the obvious stated in the manual that battery warranty may be void) of not using DVCC?


0 Likes 0 ·
Warwick Bruce Chapman avatar image Warwick Bruce Chapman mauromartini commented ·

I don’t know. But if you find out, please let me know.

0 Likes 0 ·
nigelfxs avatar image
nigelfxs answered ·
Surely I should be getting at least 3800w out of the max 4200w? Is there anything I am missing?

The rated solar power is based on "ideal" conditions with 1000W/m^2 illumination from the sun.

Your actual solar production is also affected by the mounting angle, mounting direction, temperature and your location (latitude). It is also worth checking that there is no shading of any part of the panels.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·

I would agree with that, were it not for seeing a very clear flattening off as a result of throttling on the graphs. The peak potential of the panels is not being reached.

0 Likes 0 ·
nigelfxs avatar image nigelfxs Warwick Bruce Chapman commented ·

Another possibility is thermal limiting if mounted without proper ventilation.

The "flattening off" of the current curve could also be due to clouds? I have also seen similar odd graphs when a shadow just catches the edge/corner of a panel. It's easy to overlook the potential impact of panel shading, especially as seasons change. I once had temporary shading from a tall crane from a neighbouring construction site!

0 Likes 0 ·
mauromartini avatar image mauromartini nigelfxs commented ·

At first it did actually get very hot (still only up to about 3350w). After that I put a small fan and it is barely warm now.


On the days in question there were no clouds at all. Perfectly clear.

0 Likes 0 ·
aaronsb avatar image
aaronsb answered ·

What's your DVCC maximum charge current set at? Can you post a graph of DC voltage/amperage for the same time period of your battery as well?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mauromartini avatar image mauromartini commented ·

It is not limited at all.

Correct one needed?

0 Likes 0 ·
petajoule avatar image
petajoule answered ·

I'm not sure I understand the problem here.


You write you have a MPPT 15/70-Tr.


I assume you do have a MPPT 150/70-Tr. I also assume you have a 48V system. The MPPT is able to charge with 70A max.


48V * 70A = 3360W


You get 3350W - where is the problem?


9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·

70A charge current is not the constraint in this case because feed in is enabled and the battery is fully charged.

0 Likes 0 ·
mauromartini avatar image mauromartini commented ·

@PetaJoule you are assuming dc output.

I am referring to PV yield. Panels are 4200w and my mppt is 4000w rated.

I actually got up to 3700w today turning DVCC off

0 Likes 0 ·
Show more comments
mauromartini avatar image mauromartini commented ·

The problem is I have 4200w of panels and a 4000w MPPT so I am wasting power.