Multiplus II 48/5000 additional Charge Power

Hello,


is there a possibility to use additional 48v Charger in system?

maybe it is possible to messure with 1phase sensor? To get correct soc?


best regards

Multiplus-IIcharger
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

There are a few considerations here, such as can the batteries take more charge than what the multi gives without being damaged? Is this a single unit system? A BMV would be able to measure the SOC for you as it counts energy in and out of the battery bank.

0 Likes 0 ·
Michael Schmidt avatar image Michael Schmidt Alexandra ♦ commented ·

Yes the batterys are 840Ah at 18s. They can take 1c (so nearly 50kw).

yes it is single phase with only one MP II 48/5000.

The 5kw load is more than needed but the charging power (20kw Solar Generators) could be higer.


the System also has ccgx and EM-24 so will the BMV integrate in ccgx?


0 Likes 0 ·
1 Answer
ben avatar image
ben answered ·

You can add a separate battery charger, yes. If you want accurate battery monitoring in that case, you'll need a measuring device like BMV-712 or SmartShunt at the battery terminal.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michael Schmidt avatar image Michael Schmidt commented ·

Hi ben,


adding a shunt would be a great solution.

is it possible to integrate a shunt in the Battery Monitoring of Multiplus II or maybe the ccgx? Is it maybe possible to use https://www.victronenergy.de/accessories/current-transformer-for-multiplus-ii#pd-nav-image

this to messure the additional charging power?

0 Likes 0 ·