The Cerbo GX manual says to use a 1A fuse, but the Fuse that came with the unit is rated at 3.15A (model written on the Fuse: F. T3.15A E250V P).
What is the correct replacement fuse I should purchase?
Thanks!
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
The difference between a 1 A and 3 A fuse is negliable from a safety perspective. But the 3 A is superior, it has less resistance, less voltage drop, and more tolerance for a less than perfect connection, so it’s better to use it, but 1A will still work.
In this case when there is a current limited supply, it is less important, but I would never say a fuse is pointless, its purpose is in the event of a fault.
The correct fuse size is 3.15 Amp.
There was a mistake in the original manual, it has since been corrected in the master and should be published Monday.
Did the supplied fuse blow somehow?
Thank you for the information Guy... and thanks for the private email as well!
The "slow blow" part in the manual was correct, right? So 3.15A Slow blow fuse?
BTW, no, the fuse is not blown. Since this is on a boat that is often away from shore, I always like to have spares on hand! :-)
Slow blow is better if you can find it. But a fast blow will also be acceptable as a substitute if necessary.