Good day,
For a complete OFF-grid system we want to have the following configuration:
a) 3 * Quattro 48V 15kva in parallel
b) on the DC battery side 12 Smart Solar MPPT 250/100 each connected to 5.5kW of panels each (total of 66.6kW of DC power on the pv side)
c) LiFePO4 batteries, 100kWh, 52V, Max cont. charge and discharge current: 2 000 Amps
d) 3 phases 60kva genset on AC 1 of the Quattro (with dynamic current limiter activated)
e) everything controlled by a Venus GX, use the two outputs to start/stop the genset and disconnect some non critical loads in case of low battery level
Three questions:
- is it at first feasible? I indeed saw so far a max of 8 MPPT connected to the DC side, will it then be possible to configure the entire solution with Victron's softwares?
- will the fact that DC charging power on the MPPT side is higher than the charging power on the quattro side be a problem?
- can i couple all quattro and MPPT on the same DC bus (each equipment will be fused protected of course prior reaching the bus) was thinking about a standard bus bar, otherwise having 4 Victron Lynx Distributor + lynx shunt + lynx Power In, but then i am limited to 1000 Amps on the bus bar (where we can potentially reach 1200)
Alternative would be to remove 3 MPPT250/100 and add 3 Fronius 5kva on each phases or 1 Fronius 20kva three phases (we might then have issues with the balancing of the phases except if the 3 quattro can correct this).
Thank you