Is it possible to set up a 3p configuration, where only one of the Quattros/Multis has GRID (because the grid is 1p)?
Ideally within an ESS system.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Is it possible to set up a 3p configuration, where only one of the Quattros/Multis has GRID (because the grid is 1p)?
Ideally within an ESS system.
You might want to edit you post to clarify Phase, or Parallel.
Hi @PetaJoule. I assume you mean a 3phase system, with single phase grid? This is possible, inside Ve.Bus systems configurator, untick “switch as group”
Hi @PetaJoule
Yes this is possible, but not with an ESS system (due to grid-code rules)
Please read the manual and disclaimers here also:
https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems
14 People are following this question.