1p to 3p configuration?

Is it possible to set up a 3p configuration, where only one of the Quattros/Multis has GRID (because the grid is 1p)?

Ideally within an ESS system.

3 phase
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

You might want to edit you post to clarify Phase, or Parallel.


0 Likes 0 ·
2 Answers
Murray van Graan avatar image
Murray van Graan answered ·

Hi @PetaJoule. I assume you mean a 3phase system, with single phase grid? This is possible, inside Ve.Bus systems configurator, untick “switch as group”


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

petajoule avatar image petajoule commented ·

Thank you. Is there any further documentation on this? Does one connect just one of the Multis/Quattros - or all of them to the same (single) phase of the grid on AC-In?

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @PetaJoule

Yes this is possible, but not with an ESS system (due to grid-code rules)

Please read the manual and disclaimers here also:

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems