question

daren-connor avatar image
daren-connor asked

SOC in VE Bus is not matching the battery

I have 3 x 48/5000/70 multiplus in a 3 phase configuration which is fed by a 15kw Fronius 3 phase solar inverter.

Lately the SOC in VE Bus does not match the batteries. This causes the SOC to stop st 90% SOC when the batteries are at 57.6v which is the absorption voltage. Sometimes it will sit at 90% for 3 or more hours waiting for the batteries to meet the SOC before going into absorption. I've tried everything I can think of but I'm obviously missing something. Even my installer is at a loss. Can someone please help. Thanks in advance...

battery chargingSOCVE.Bus
8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daren-connor avatar image daren-connor commented ·

It gets to 90% SOC but the batteries are only 55v so it waits at 90% until the batteries reach the absorption voltage of 57.6 then it finally starts absorption. Any ideas?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ daren-connor commented ·

@Daren Connor

Are these batteries with their own BMS or managed only through the VE Bus?

0 Likes 0 ·
daren-connor avatar image daren-connor Alexandra ♦ commented ·

Managed only through VE Bus. All firmware is the latest on all 3 multiplus & the ccgx.

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ daren-connor commented ·

Since I dont know many details about your install. We start with basics which is are the battery cables the right size for the system? The most common cause of what you are describing is voltage drop. Or extra resistance points along the cable such as breakers or fuses may be causing an issue. Are you using a lynx shunt or any thing like that?

0 Likes 0 ·
daren-connor avatar image daren-connor Alexandra ♦ commented ·

It's been running fine until I had a complete shutdown one day when the generator shut off under no load so I was told to update the firmware in the multi's & that will fix that problem, which it did.

Since updating the firmware it has been doing what I stated. I've had this system for over 5 years & it has never missed a beat until the firmware update. I even rolled back the firmware to a previous version but that didn't help either. It's like the batteries aren't synchronizing with VE Bus anymore..

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ daren-connor commented ·

It seems must be settings then. Were the previous settings kept from before the firmware update and then reloaded; or was it treated as a new install?

0 Likes 0 ·
daren-connor avatar image daren-connor Alexandra ♦ commented ·

The previous settings from what was working were saved & used to reconfigure the system after the firmware update.

0 Likes 0 ·
daren-connor avatar image daren-connor Alexandra ♦ commented ·

The original firmware was 2624209 which has now been updated to 2624459. What are the main differences between these 2 firmware versions?

0 Likes 0 ·
1 Answer
Mark avatar image
Mark answered ·

Most likely your current battery monitor settings in VE.Configure are inappropriate for your battery bank.

Regardless what settings you expect have been copied over from the original FW, as the new FW is so much newer maybe that didn't totally work.

Specifically check the 'battery capacity' and the 'charge efficiency'.

It is likely that the battery capacity is set too low and possibly charge efficiency is set too high.

There is a setting 'state of charge when bulk finished' and it sounds like you have it set to 90% SOC (which is reasonable) - so the battery monitor is correctly following this logic. The issue is that it's not accuracy tracking the batteries true SOC % well.

Lastly, do you have any DC loads powered by the same battery bank? As the VE.Bus battery monitor would not consider these loads in the SOC % calculations.


12 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daren-connor avatar image daren-connor commented ·

I have a 1350ah lead acid battery bank, it's set at the default charge efficiency of .95 & bulk finishes at 90%.

These settings worked perfectly well in firmware 209 but for some reason in 459 it holds at 90% until the batteries get from 55v to 57.6v. That can take up to & even over 3 hours.

The system was actually working perfectly with 209 until a problem occurred during a generator shut down & a victron representative told me to update the firmware which did fix that problem but created a much worse problem. That was over 3 months ago & I'm still battling with it. I've adjusted charge efficiency, charge rates, even adjusted the PV assistant but nothing ever changes the fact that the batteries & VE Bus are not synchronizing. I'm at a complete loss.

0 Likes 0 ·
Mark avatar image Mark ♦♦ daren-connor commented ·

So you have confirmed that 1350Ah is programmed in the battery monitor - correct?

In your case, next step I recommend is to perform a proper full charge cycle so that the battery really gets to 100% SOC and you have a proper synchronised baseline for the battery monitor to work with going forward. To do this you may need to temporarily change to 'fixed absorption' time and keep charging at absorption voltage until the charge current flowing into the battery tails off to about 1% of your battery capacity (so about 13.5A).

Also, how far down do you normally discharge the battery each day? If not much/only to ~85 or 90% SOC, it might be more accurate (for your usage profile) to try increasing the 'SOC when bulk finished' setting to ~95% SOC.

0 Likes 0 ·