Multiplus ii 48/5000 G98 Compliance

Slightly confused by Multiplus ii 48/5000 G98 Compliance.

The certificate covers both 3000 and 5000 models and states for "Fully Type Tested Micro-generators (up to 16 A per phase)

https://www.victronenergy.com/upload/documents/Certificate-G98-1-MultiPlus-II-48-3000-35-32-&-48-5000-70-50-and-MultiPlus-II-48-3000-35-32-GX.pdf


ENA shows the 5K as over 3.68kW (as expected):-

https://www.ena-eng.org/gen-ttr/Index.aspx?Action=ViewDetail&EID=34144054&tab=search


Is the certificate incorrect, or when configured is there a restriction in ESS limiting grid export to 16A?


Thanks!

ESS
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

xtopher avatar image xtopher commented ·

Just resurrecting this thread as I am looking into G98/99/100 compliance as I am considering a Mutliplus II (likely the 3kva) for my house here in the UK along with Pylontech batteries. I can see that it has G98 and G99 compliance certs on the website, but interestingly I found a PDF on a UK supplier that suggests it can also be G100 (limited to 3.68kW grid supply) - https://midsummerwholesale.co.uk/pdfs/victron-g100-declaration-multi.pdf


What I am wondering is can this also be achieved using a Multiplus II GX with the optional CT clamp on the grid connection (https://www.victronenergy.com/accessories/current-transformer-for-multiplus-ii) rather than a wired AC sensor in the main consumer unit and Color Control CCGX? I only have a single spare way in our CU which would not facilitate having a wired AC sensor without replacing the CU or possibly moving some circuits around.


Also does anyone know with UK rules if it is acceptable to have an electrician commission the circuit for the Multiplus, but DIY install the Multiplus and batteries yourself? I understand it wont be MCS accredited and thus not able to get SEG payments but I am not looking to do that as I want to only buy electricity at cheap rate to charge the batteries and consume the energy myself.

1 Like 1 ·
awalkerinuk avatar image awalkerinuk xtopher commented ·
I am in the England and have installed the multiplus ii myself, have done all of it including ET112 meter.

Then went on the DNO website UK Power networks and had it approved.

Not an Electrician but was happy to do it myself. Dont know if its accepatable under UK regs but like doing things myself to cut costs.


0 Likes 0 ·
jonaaal avatar image jonaaal awalkerinuk commented ·
What did you put for "Installer Accrdiattion/Qualification"?

Did you submit a G98 or G99?

Did you submit a G100 type approval certificate number?


Asking because I am planning to do this (with a qualified electrician) very soon.


0 Likes 0 ·
awalkerinuk avatar image awalkerinuk jonaaal commented ·

Uk Power networks online form did not ask for an "Installer Accrdiattion/Qualification"? Just wether I was the home owner or an installer

G98 submition.

G100 approval was put on by uk power networks engineer themselves. So dont know of a number for it.

Sorry for the late reply


0 Likes 0 ·
spanner avatar image spanner commented ·
I did read on the numerous threads there is a G98/G100 that if the system doesn’t feed back onto the grid then it’s split into inverter KWH and Battery KWH, need to locate the article!

ps I’m in the same position to press the button on a 48/5000 as well.

0 Likes 0 ·
spanner avatar image spanner commented ·
0 Likes 0 ·
johnone avatar image johnone spanner commented ·

No - that's kiwa issuing a 'certificate'. It's then up to the regulatory authorities to decide if they agree with kiwa - currently, in the UK, ENA don't agree and say 'further information required'. However, ultimately it's down to your electricity distributor (DNO) - the company which owns and controls the distributed grid network - to decide what is connected to their network. Currently, there are lots of examples of DNOs agreeing to Multiplus-II based systems being connected. The best thing to do is contact your DNO.

0 Likes 0 ·
7 Answers
ejrossouw avatar image
ejrossouw answered ·

In an ESS configuration, you have the option to adjust the grid setpoint to zero which means practically no feed-in. That in conjunction with the "don't feed-in excess solar power" e.g. MPPT means you can have a self consumption only system.

Why do you need a larger charger? Lithium charges very fast and using a DC MPPT charge controller you can use a larger charger. I charge my LG RESU 10 in under 4 hours from a 90% discharge state on my Mult II 3000VA. It is used without solar and set up for self consumption grid parallel. See here http://essandsolarsolutions.co.uk for an explanation. I have used this to cut my monthly electricity bills by 50%.

Ultimately it will depend on your actual consumption pattern, Wh and then requirement.



1582983415509.png (34.6 KiB)
ess-system.jpg (32.9 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrisgla avatar image chrisgla commented ·

Thanks, my planned use isn’t too different from yours, but Pylontech 7kWh and Agile. Think charge will be around 3hr @35a. 70a was more future proofing in case I expand battery.

Thinking about MPPT, but solar’s hard to justify in the North. That said, I have 400w 24x7 for pond for six months a year- so I may add 2kW of solar. Total daily is around 15kWh.

I already have EV Charger with Modbus charge control, but not using it too much yet. Plan is to get that and batteries onto similar schedule to you Through Cerbo and local plc.


Thanks for your help- like the roof on your site! Would be great for rain-bathing here though...

0 Likes 0 ·
ejrossouw avatar image ejrossouw chrisgla commented ·

With the newer generation mono panels you will be surprised how sensitive and efficient they are. I have been looking at defining a solution for someone up north who produces 56kWh in a day, but FIT is not worth it as he also has an EV. Look at the Jinko maxim maybe as they have integrated optimizers for each cell string in the panel.

The room above the garage has a 600mm diameter concrete post for a telescope so it is actually an observatory which is why it slides open ... no longer used for that but soon to be my star bar and lounge. Sadly I only spend a couple of weeks there, but is is totally off grid with only a 4k battery and works.

0 Likes 0 ·
ejrossouw avatar image
ejrossouw answered ·

Hello @chrisgla

My take on it is. Yes, you can limit the inverter output, however, only if the below is adhered to will the MP II 5000VA (4000W) be GS98 compliant. It otherwise, if you disregard the generating capacity, meets the technical Type Testing standards for GS98 & GS99.

"The Manufacturer may restrict the rating of the Micro-generator by applying software settings provided these settings are not accessible to the Customer"


1582882575270.png (37.8 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrisgla avatar image chrisgla commented ·

Thanks, but that doesn’t look like it limits export power, it appears to limit the total inverter output instead?
The point of G98 with G100 is to allow self consumption + export to use more than the 3.66kW limit of G98 without significant oversight.

I’m exploring this from a number of perspectives, but there would seem to be benefit to having a UK G98/16a export limited country code/ ESS template . That’s would then seem, more easily manufacturer locked than the above?

A second template for compliance covering 16-19a (or more for parallel) export might be useful


48/3000 doesn’t have this issue, but charging is less.

Pity, the cost of witnessed approval, etc above 16a is basically making system unviable.

0 Likes 0 ·
sharpener avatar image
sharpener answered ·

Hi @Xtopher

I am in a similar position to you but in addition I already have 2 x 2kW Steca AC inverters with 3.68kW of solar panels.

I would like to add an EasySolar II 48/5000 (which is electrically almost identical with the MP-II), with another 3 to 4 kW of panels connected to its MPPT and 8kWh of LiFePO4 batteries.

AIUI if there are no AC loads or sources on the AC-In side of the inverter then its internal current sensing should be adequate, failing which I can't see why you would need more than the CT accessory.

You also wrote <Also does anyone know with UK rules if it is acceptable to have an electrician commission the circuit for the Multiplus, but DIY install the Multiplus and batteries yourself?>

It's hard to see how a self-install can easily comply with "The Manufacturer may restrict the rating of the Micro-generator by applying software settings provided these settings are not [readily] accessible to the Customer".

The rest of what you are trying to do is probably covered OK by the "Fast Track" G59 approval process, as in inverter mode the MP 3000 can only generate 11Amps, and fail safe operation is not mandatory below 16A so you may not need the G100 declaration.

Unfortunately I need the ES 5000 version as I need the 50A pass-through capability, and since this model can export 19A it opens up a whole new can of worms even though it can be limited to 16A or indeed zero. Looking on the Western Power Distribution web site I cannot see an easy way forward and I am awaiting a callback from them. They also appear not to allow island operation, even though the inverter has an internal anti-islanding relay and grid failure backup is one of its features.

If I learn anything more from WPD or the wholesalers I will post it here.

It would be good if someone from Victron is watching and could post something authoritative about how to comply with the UK regulatory system.

HTH

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image ejrossouw commented ·

"For Power Generating Modules with an aggregate capacity < 50 kW 3-phase or 17 kW single-phase, this simplified application form can be used. For Power Generating Modules with an aggregate capacity > 50 kW 3-phase, the connection application should be made using the Standard Application Form (generally available from the DNO website)."

G59 is no longer so I'd advise to get up to speed with the latest G98/G99 requirements which also include AC coupled batteries. Type testing G98/99 merely indicates the device conforms to the parameters set by the DNO for generating devices to be connected to the national grid (UK) and not not cause interference, complies with anti-islanding rules, etc.

My understanding is the DNO is interested in the total aggregate generating capacity of all the connected devices regardless of limiting functions given in a fault scenario they will have to ensure the network/substations etc. can handle the additional power. G100 will likely need expensive hardware the DNO can set and control or them observing ompliance testing, but I do stand to be corrected and cannot speak for any DNO.

When adding capacity it may become more of a challenge as opposed to new installs, but then your DNO will be in touch to discuss the application and their responses are seldomly aligned across regions. None of my DIY customers were ever told by a DNO they were not qualified to do an install of a type tested Victron inverter, but I cannot stress enough that work carried out has to comply with Part P building regulations in this regards and yes there is a difference for e.g. Wales. New circuits will require a qualified electrician to install it and do the relevant notifications.

My personal view on settings being protected by a seller/dealer is that is will be highly unlikely especially in a DIY install and even the systems I access for my customers are fully accessible to them as it does not protect the required feed-in setting only. Most dealers simply won't be set up for it or interested or may charge a monthly monitoring and management fee.

In summary, my advice is to start by submitting the application and take it from there. The essence of it is a quality and clear diagram and then listing of the existing generating devices and additions so the DNO can determine the aggregate power as well as verify ENA type tested certification. Most of the times my DIY customers were surprised by how easy it was as opposed to difficult.

2 Likes 2 ·
xtopher avatar image xtopher ejrossouw commented ·

Thanks for the feedback that is very useful.


This will probably be useful to you with regards the G100 'compliance' (I say that loosely, I would imagine it is meant to just smooth over applications).

https://midsummerwholesale.co.uk/pdfs/victron-g100-declaration-multi.pdf

Details the bit on the password which DNO's accept (of course if you put a bit of effort in you can find the password but the layman doesnt frequent these forums and find that password). Particularly helpful with the relaxed/fast track G99 application where you can have a combination of 16A solar and 16A battery inverter/chargers but requires limiting to 16A export (seems to be officially named as 'Fully Type Tested Integrated Micro Generation and Storage'). This is what I have been referring too as fast tracked application. So its not a standard G99 application but uses a different form and allows for a faster application (sub 10 days) compared to a standard G99 application (which I think is upto 45 days?) . I will probably end up having to do a full G99 application anyway, so might just get on with it, as batteries are largely out of stock til June so have a while to get it all together.


Also worth noting, where I say DIY, I will be using a local spark to commission the correct circuit and terminate it such that I can connect up the Multiplus to it with him, so will all be Part P done officially.

0 Likes 0 ·
ejrossouw avatar image ejrossouw xtopher commented ·

If your are only installing e.g. the Easysolar-II and DC coupled PV and storage, there is only one inverter involved that can produce a max 4kW (4.4kW if in off grid mode I believe). Since the hybrid system cannot generate more than that regardless of how much DC PV or storage you add, the generator (inverter) is the part that will be approved or aggregate if there are multiples in e.g. a microgrid. When you retrofit an AC coupled battery (own inverter/charger) to a grid-tie PV system or such a new system configuration, the 2 x 16A will apply. Recently 3 of my DIY customers who did their own G99 applications and install had 5kVA Multiplus-II systems approved without any mention of G100 or limiting so, as the trend goes the DNO has bigger fish to fry than worrying about limit these "small" systems. Since these are guidelines as opposed to rules, DNOs still have room for discretion, which is why I don't speculate, but advise to submit an application and then engage in the conversation if they do actually get pedantic.

0 Likes 0 ·
xtopher avatar image xtopher ejrossouw commented ·
Thanks that's very helpful and good to know. I will be installing the ET112 anyway so to aid in self consumption so its no loss either way, and as you say, by the time we mess around, we could have put a G99 application in anyway and heard back.
0 Likes 0 ·
xtopher avatar image xtopher xtopher commented ·
Caught up with ENWL and they've advised just stick a G99 application in for 7kWp export limit and they'll sign it off. They confirmed the 'fast track' limited scheme only applies to when you have two upto 16A generators and actually the application wont be any slower just doing a standard G99 at the power I want.


One thing that was odd is he said they would want to know the size of everything, so not just generation kWh (inverter), but battery kWh and DC solar kWp, even though the only thing they actually care about is the inverter as that's what can put power back to the grid. Looking at form A1-1 there is nowhere to put the details he is talking about, only space to put the generation which would be 4.4kW for the MPII 5kVA?

I also assume should I put an application for the 4.4kW, I can add as much solar or battery behind it on the DC side as I like? As all that can ever go to the grid is the 4.4kW from the inverter. He was saying put in for 7kW now as thats what he can see would be approved with no cost, but I have no idea how you would do that, as I'd have to make up a generator or over specify what the MPII power rating is? All very weird.

I think I will chuck in the G99 application though as the two options I currently have is a MPII 5kVA or 3kVA so at least then I'll have the option for the larger one if I go that route and if I go 3kVA I can just put in the G98 notification.

0 Likes 0 ·
vincegod avatar image vincegod ejrossouw commented ·
Does anyone have a copy of an approved G99 using the Multiplus II 5KVA, of course with all the personal details redacted?


0 Likes 0 ·
xtopher avatar image xtopher commented ·
Will be interesting to see how you get on.


I am also in discussions with ENWL about the fast track G99 as their site states the limit is 7.36kW which would mean you could have the 5kVA model on its own if solar is then on the DC side rather than AC. BUT the form you then fill out from ENA mentions 2x 16A devices as a named thing so not sure it will work. Don't see why they would be bothered as the 5kVA can only put out 4.4kW sustained so well below what 2x 16A generators could do. I only bring this up as the dealer I am talking to has suggested a 5kVA and DC PV rather than 3kVA and separate 3.6kWp AC PV - which itself is G99 fast track as is 2x 16A generators. The benefit of the DC PV is that we can oversize and get a good amount of energy into the batteries and house loads at the same time as we'd be able to do 4.4kW into the house and more into the batteries at the same time (if I understand it right)


With regards the settings not being accessible to the customer - the dealer I would get it from will configure it up and send it out ready to go for our setup. I just have to wire it up and plug it in. They can remote on for any issues and the settings are then behind the dealer/manufacturer passworded part in the configuration that only certified dealers/installers/etc know (supposedly ;-) )

0 Likes 0 ·
kjhxxx avatar image
kjhxxx answered ·

Hi - I am in WPD area and although I am yet to install I submitted form A1-1 specifying a MULTIPLUS II 48/5000/70-50 and was approved based on 5KW max import on my supply. The approval states that I supply a commissioning report detailing working export limitation but that WPD do not need to witness. Hope this helps.... :)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sharpener avatar image
sharpener answered ·

Thank you @KJHXXX , that is brilliant.

I think my problem is going to be my solar PV. For "integrated microgeneration and storage" the application needs to be on Form A1-2 and there is a limit of 16A/phase for each of the two technologies.

The other issue is persuading them that the EasySolar is electrically the same as the Multi since I have not yet found any certification for it.

But if you could let me have a contact name at WPD that might help to smooth the way....

Many thanks

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image ejrossouw commented ·

https://www.victronenergy.com/upload/documents/Certificate-ESS-G99-1-EasySolar-II-24V-48V-3k-&-48V-5k-GX.pdf

0 Likes 0 ·
Show more comments
stefmari avatar image
stefmari answered ·

and yes in Victron's settings under GRID tab for 'UK: G98 and G99' grid standard' details CANNOT BE altered by anyone. These are settings set by Victron used at/for type tests.

g98-option.png

AND

g98-details.png


g98-option.png (12.2 KiB)
g98-details.png (23.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stefmari avatar image
stefmari answered ·

Hi All,

The latest (as per post's date) ENA's Engineering Recommendation G98 Issue 1 Amendment 7 (October 2022) from ENA on page 24-25 it says

https://www.energynetworks.org/industry-hub/resource-library/erec-g98-requirements-for-connection-of-fully-type-tested-micro-generators.pdf

screenshot-2022-11-11-at-160407.png


so it is quite clear that there are no particular certifications are required BUT common sense and understanding of safety rules (fundamentally important!) and manufacturer's installation rules also.


and it follows with 8.2 Commissioning with a quite simple test 'removing the supply to the Micro- generator during operation and checking that the Interface Protection operates to disconnect the Micro-generator from the DNO’s Distribution Network'.

screenshot-2022-11-11-at-161248.png


The above test it is very important as if completed successfully the test proves that in case of DNO's loss of supply the inverter islands (it is not anymore AC Grid Tied!)

This is a SAFETY. Why? imagine what can happen if your 10kw or 20kw storage batteries can still feed in DNO network after DNO loss of supply. Once DNO loss of supply is detected inverter cannot stay AC Grid Tied-in. The inverter shall switch back from island mode to ac grid tied-in only after DNO restores supply.