It only show starting but does not proceed in equalisation, i’ve checked the firmware and up-to-date I have a multiplus 48/5000/70, solar charger in Mppt 150/85
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
It only show starting but does not proceed in equalisation, i’ve checked the firmware and up-to-date I have a multiplus 48/5000/70, solar charger in Mppt 150/85
Hi; has this been resolved in the mean time? If not; please list the firmware versions that you are using.
@mvader I have a similar/comparable problem with Easy-solar 48/5000/70. As my lead-acid cells are seriously getting out of sync I wanted to perform an equalizing cycle. It was refused (charger not ready). I presumed that (logically) you need full charge to do so, and I changed my settings from 70% minimum SOC to 100%, waited for 100% to display to again get the same message. Further on, although 100% charge is displayed the bulk led stays on.
https://vrm.victronenergy.com/installation/31525/share/c43e4823 for any information on firmware (it should all be the latest)
Hi @josmeijer, did you try setting the ESS mode to 'keep batteries charged' first?
Nee, en dat was 't dus.....
@josmeijer,
Perfect, thanks for the feed-back
Fijne jaarwisseling!
I have the same problem @Potgieter. Hangs on "starting" when I try to run equalisation from the CGX. I've also tried using the switch sequence on the front panel buttons. Charger was in Float mode, firmware up to date. Has anyone found a solution?
Easysolar 48/5000/70-100, CGX, BMV, lead acid batteries, off grid with solar input only.
If you don't have AC input, you have to equalize with the MPPT, not with the inverter (Multi)
See manual of MPPT for how to do this.
Good morning Daniel,
thank you for this information. but how we can Eqlz via MPPT when this is in ESS mode and controled via Multi+CCGX
before ESS we have the possibility to config the MPPT with the App every 15 or 30 days Eqlz automaticaly but now we do not have this funktion yet.
If we can add this time setting to the CCGX and make sure the manuely Eqlz, it will be a very good tool as like the MPPT
many thanks and BR
HuHu
Hi HuHu,
An off-grid system = not an ESS system, in an ESS system your Multi / Quattro does the equalizing, in an off-grid system the MPPT's (or when you have a generator, you can use the Multi)
Thanks for your discussions, which explain why my equalisation is not working (offgrid). Please can you show me where I can run the equalisation from the MPPT menu?
Hi Gavin, is this not in the manual?
I can find manual entries for the stand alond Blue Solar MPPT controllers, which indicate that equalasation can be started through Victron Connect. The MPPT in the EasySolar does not appear to be compatible with Victron Connect. The only access I have to MPPT options is through the CGX, which has no options for equalisation.
The MPPT in the Easysolar is compatible with Victron Connect.
You'll need a ve.direct - USB cable to configure if you don't have the 'Smartsolar' with bluetooth.
But as you'll have configured the MPPT I assume you'll have that cable already?
Thanks Daniel. Apologies for stupid questions; I am a user of this technology, not a technician. But I need to learn it as I am fairly remote.
I think I understand now. My MPPT does not appear to have bluetooth, which is why I was saying it did not seem to be compatible with Victron Connect.
I don't have a cable since I didn't do the installation. I recently discovered I need a MK3-USB cable in order to update the firmware on my Multiplus. Can that be used for the MPPT as well, or do I need to buy both cables?
8 People are following this question.