According to install manual, a DOUBLE pole fuse/breaker is required on the AC input to a 12/2000 multiplus in a 30 amp circuit. Is this correct? Or could I use an inline fuse?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
According to install manual, a DOUBLE pole fuse/breaker is required on the AC input to a 12/2000 multiplus in a 30 amp circuit. Is this correct? Or could I use an inline fuse?
IMO it is highly recommended to use a double-pole circuit breaker.
If you have two hot wires (2x120V) and there's a problem on one of them, the double-pole circuit breaker shuts down BOTH wires. That does not happen, when you fuse each of the wires independently.
@Davis Kyle, you need a double-pole breaker for your "shore power" input; a fuse is not appropriate.