According to install manual, a DOUBLE pole fuse/breaker is required on the AC input to a 12/2000 multiplus in a 30 amp circuit. Is this correct? Or could I use an inline fuse?

fusesmultiplus compact
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

IMO it is highly recommended to use a double-pole circuit breaker.
If you have two hot wires (2x120V) and there's a problem on one of them, the double-pole circuit breaker shuts down BOTH wires. That does not happen, when you fuse each of the wires independently.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Justin Cook avatar image
Justin Cook answered ·

@Davis Kyle, you need a double-pole breaker for your "shore power" input; a fuse is not appropriate.