question

michelp avatar image
michelp asked

Multiplus-ii - PV power incorrect - how to configure PV location

I have some issue on power indicators in my Multiplus-ii Gx

My system:


No break loads =0W, Loads=0W

When i ask the remote console I get:

The Grid Find-in is arround Twice the PV Power and the Grid value on the Gx LCD is arround -600W

I assume the Grid value on the LCD is the ACin1 measurement

So why there is Power that is feed from the Gx ?


Multiplus-II
test-passthru.png (28.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
warzel avatar image
warzel answered ·

It is fixed. Setting the PV inverter to AC Output fixed it

Settings -> PV inverters -> Inverters -> AC-OUt L1 -> Position -> AC Ouput


fine.png


fine.png (26.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @michelP

You've configured the PV inverter on the input, but you have to configure it on the output in the settings.

everything 'behind' the current sensor is measured as on the output of the Multi.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

michelp avatar image michelp commented ·

Hi @Daniël Boekel (Victron Energy Staff)

To be shure on my understanding I need to move my PV to the ACout (only in the software) there are still connected to the AC_in

Does this apply also for the loads ?

I have move the PV to output and it's ok

But for the lood that are on mains this is'nt good

Does this rule also for the loads ?

Michel

0 Likes 0 ·
test-passthru2.png (30.1 KiB)
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ michelp commented ·

Hi @michelP

Please read the ESS manual first:

https://www.victronenergy.com/live/ess:design-installation-manual


Also: your system is in pass-thru, is that intentional or is something wrong?

0 Likes 0 ·
Show more comments
warzel avatar image
warzel answered ·

@michelP did you ever got this solved ? i have the same situation. The PV is physically connected to 'AC-out-1' and in the ESS assistant i configured a PV connected to 'AC out'. I use the internal power meter of the Multiplus II GX. There is nothing connected on the 'AC-in' side , accept the Grid. But i also see double the solar power display in the console app feeded back to the grid. The display on the MultiPlus shows the correct power feeded back into the grid. Exactly your issue.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources