Hello
My MPPT 75/15 Smart Charger does not cut off load when reaching low level set.
Why could this be?
I've activated user defined Algo 1 and se 25.00 V and 28V but not cutted even 24.8 reached...
Any hints?
FW: V1.46 and V2.23 Bootoader V1.10
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hello
My MPPT 75/15 Smart Charger does not cut off load when reaching low level set.
Why could this be?
I've activated user defined Algo 1 and se 25.00 V and 28V but not cutted even 24.8 reached...
Any hints?
FW: V1.46 and V2.23 Bootoader V1.10
Did still not work.
Now I've compared all values from an other one I have 100/15 charger and this one has
Rx port function: "Load output configuration" as default
where new one had other one, I don't remember which one :-(
I think it was "Load output on/off normal"!!
I have not set this value on the other one, so this seems to differ from this 2 models
or old fw version....
Where are the infos about this configurations?
I've also removed the jumper is on the VE.Direct connector as mentioned in an other post.
And yes de delay is exactly 2min after reaching the state to power off or on.
I thought the delay was if you change the configuration, but it is applied everytime a state change is reached...
4.5 Rx port function
https://www.victronenergy.com/live/victronconnect:mppt-solarchargers