Hello
I've an Victron Smart Solar Charger 75/10 and 2x12V EVH12390 CSB Deep Cycle AGM Batteriees and and 48V DC Power Supply (as mentioned in other post) and it works great as Inteligent Battery charger!!!
I'm in doubt about setting values for the battery on/off levels and charge configuration.
From the net I've found the following values:
State of Charge Sealed or Flooded Lead Acid battery voltage Gel battery voltage AGM battery voltage
100% 12.70+ 12.85+ 12.80+
75% 12.40 12.65 12.60
50% 12.20 12.35 12.30
25% 12.00 12.00 12.00
0% 11.80 11.80 11.80
Deep Cycle
State of Charge 12 Volt battery Volts per Cell
100% 12.7 2.12
90% 12.5 2.08
80% 12.42 2.07
70% 12.32 2.05
60% 12.20 2.03
50% 12.06 2.01
40% 11.9 1.98
30% 11.75 1.96
20% 11.58 1.93
10% 11.31 1.89
0 10.5 1.75
Now my battery has the following specs:
So from the Battery Voltage and Charge time for Cycle Use I interpret that 70% charge level is at 1.9V which would be 11.4V
which from the table above gets 2.05V per cell i.e. 12.3V and this is a big difference...
Does I interpret something wrong?
(My load is only about 1-1.5A max at 24V)
Nevertheless connecting to solar charger after full charge with a normal charger my batteries have 26V i.e. 13V beginning test with 0.6A load after 1.5h still 25.73V i.e. 12.87V so I'm pretty confused about 100% values etc....
Any hints would be nice :-)
I want to discharge my battery about 40% max. to get good battery life or can I use 50% for Deep Cycle batteries without problems?
The application is from a tower with communication equipment...
I too want if the output cuts off because low battery, that it goes on after short period of loading the battery.
(if there was a power loss over long period and batteries were drained, I cannot wait hours to go online for my system)
What would be a good Load switch high voltage level?
If I load batteries with 10A/24V and there are 24V/39Ah at a level of 50% discharge (20Ah) I guess the batteries would be charged in 2h.
So if the table is right with 50% 2V I have 4% charge in ten minutes (120min 50%)
So cutt off 50% would be 24V and 24.4V on or should I set less than 24.4V?
As mentioned I want to go online not more than 15min after power comes on
Here my current configuration: