I have a 5000/70 multi, 4 kW Fronius on ac1 out, a 250/70 smartsolar on dc bus and 2xEms48100 li-ion batteries.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a 5000/70 multi, 4 kW Fronius on ac1 out, a 250/70 smartsolar on dc bus and 2xEms48100 li-ion batteries.
If the Smartsolar and MultiPlus are not in an ESS system (with a CCGX or VenusFX etc.) then they will operate independantly, running their own algorithms.
In that case you can expect each charger to switch to different charing stages at different times.
Sorry i left out the ccgx. All connected to it. ESS assistant present
13 People are following this question.