Hi Guys,
We have 1 x Quattro 48/10000 with 5 x Redflow Batteries. The site is on Grid only (no solar) with generator backup. ESS is enabled (ZCell and Venus talking via Can Bus)
The Grid is limited to 35 Amps and the generator to 120 Amps. I have instructed the Victron to "keep batteries charged" and set the min. SoC to 50%.
The Victron seems to never want to charge at any rate and prefers to suck energy from the battery.
Also, our grid has a set point of 50W - not sure if this is relevant :)
How can I this "fixed" - I want to limit Grid to 35 Amps, keep the batteries at 50% and if needed, use PowerAssist to get the rest from the batteries.
or - How can I debug this - something must be saying not to charge ?
Thanks ! :)