question

Matt Knight avatar image
Matt Knight asked

Powering BMV-712 from 12V UPS

We have an off-grid installation in our RV with LiFePO4 batteries along with a 3kVA Victron MultiPlus, CCGX and BMV-712. The behavior of the BMV-712 is such that if it loses power, it restores to 100% SoC when turned back on. I am aware of the setting so it is set to unsynchronized instead.


Unfortunately neither behavior is suitable for us - the most likely cause of loss of power to the BMV is the BMS temporarily cutting off the batteries due to excessive current. This is a temporary situation which we can restore from within about 1 minute, so the SoC of the batteries does not change meaningfully during this time.


My plan is to install a 12V Uninterruptible Power Supply (UPS) that is kept charged by the main batteries but provides reliable power to the BMV as well as a handful of other low power but key systems such as the TPMS booster and probably the CCGX. I have a Blue Sea Systems split fuse block and the UPS will power the bottom section for these devices.


We have recently acquired the temperature sensor to connect to the BMV-712, and this has two wires - essentially data and positive power. I'd like to connect it such that the data line goes into the BMV but power for the BMV comes from the UPS into the other connection on the BMV. The temperature sensor draws its power from the 12V positive terminal it connects to, but I will remove the fuse and not connect its power line to the BMV.


I have tested this by connecting it up and it all seems to work correctly. However, before I hardwire this in, I wanted to check to see if a) anyone can see any reason this wouldn't work in all cases (I haven't checked all failure scenarios) and b) there are any plans to add a capability to the BMV-712 to restart with the last known SoC.


Thanks in advance.

BMV Battery Monitorups
8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

markus avatar image markus ♦♦ commented ·

Hi,

It could work, to use the starter battery over a relay or some combiner, switching, to supply power to BMV in case of LiFePo goes off. Just thinking...

If the BMV is not supplied by the batteries voltage, SOC calculations will be incorrect.

The Multi can calculate SOC based on his own consumption, if you have other DC loads, the Multi can't measure them.

Regards,

Markus

0 Likes 0 ·
Show more comments
1 Answer
wkirby avatar image
wkirby answered ·

Are you intending to have the BMV permanently powered from the UPS? It would work of course, but in that case it will not be passing true Voltage values to the rest of the system. You could set the MultiPlus to be the system Battery Monitor, but then the BMV would be a bit redundant.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matt Knight avatar image Matt Knight commented ·
@WKirby Yes, I would need to use the MultiPlus as the voltage monitor. The BMV would still be doing a valuable role monitoring the SoC of the batteries as we have Lithiums so need to Coulomb count - that's where the BMV's shunt would come in.


I would imagine the MultiPlus voltage measurement would be incredibly close to that of the BMV, right? The batteries are connected to the MultiPlus with a short length of 4/0 cable, so if anything the voltage drop is probably higher along the thin power cable of the BMV's temperature probe.

0 Likes 0 ·