Bypass mode?

Hi,

Is there a bypass mode to activate when one would like to externally bypass the inverter (Quattro) for example when to service units ?

My Eaton UPS has this mode when i shall bypass it, it helps me switchover without downtime.


Kind Regards

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Tom avatar image
Tom answered ·

Yes you use your Mk3 and turn off both inverting and charging. This way you can just use your plugged in shore power or generator.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ehsab avatar image ehsab commented ·

I don't think you understand the question, i would like to switch the current to not flow via the quattro at all.

0 Likes 0 ·
Tom avatar image
Tom answered ·

I think you would need to install an external transfer switch to do that. It is less costly to turn off charging and inverting or run a second AC out 2 that bypasses the quatro inverting .

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ehsab avatar image ehsab commented ·

Yes i will install an external switch.