question

Pete Lambert avatar image
Pete Lambert asked

Easysolar 48/5000va/70 SoC always 100%

Hi all, my CCgx panel always displays 100% battery even when voltage drops to 48 and below. I have 8x 6v AGM 550amp batteries and No grid input, purely 4kw of pv panels for an input of 120v (4 in series x 4)

I have updated all firmware to current (2020) versions with no change

ESSCCGX Color ControlEasySolar All-in-OneSOC
8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Pete Lambert avatar image Pete Lambert commented ·

My battery settings in Victron connect app on the smartsolar have been set as follows

Absorbition 57.6

Float 54.4

Equalization 59.2

These figures I took from the battery specs and multiplied by 8. Seemed the right thing to me but maybe wrong

0 Likes 0 ·
Murray van Graan avatar image Murray van Graan commented ·

Hi @Pete Lambert, do you have an external battery monitor installed, or are you using the battery monitor function of your inverter/charger?

0 Likes 0 ·
Show more comments
1 Answer
ejrossouw avatar image
ejrossouw answered ·

@Pete Lambert Is your system connected to the VRM portal? If so, you can configure the unit by downloading the config file (under device list) and using ve.config to adjust and then upload again.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.