Is a second RCD required or recommended?

I have a Multiplus II. I have it set up with AC out 1 as the only AC output and run it in a grid parallel configuration (power is monitored with an ET112 meter). The power goes through an RCD (Earth leakage and overload) and then splits. One split goes to the AC in of the inverter (Critical loads), the other to the parallel loads (Non-critical). I have a 23A circuit breaker after the inverter, Do I need an RCD after the inverter?

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

Yes, because the RCD at the input is useless if the grid is not available.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

solarhack avatar image solarhack commented ·

Thanks, That is what i thought