MultiPlus charge settings for third party LiFePO4

I've got a 8S LiFePO4 with an internal BMS (I can't tap into it). For LiFePO4 and other lithium chemistries, I'm used to a CC/CV (constant current then constant voltage) charge cycle. What I would like is to get the MultiPlus to charge at no more than 50A until it hits 28V (3.5V per cell) (then hold that 28V until the charge current drops to 5A. I don't want any float stage or any periodic re-absorb.


Could someone give me advice on how to get as close this as possible?



Multiplus-IIbattery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

Give this a go and see if it helps

limit the charge current to max amps of 50 amps and set the float voltage to say 24 volts or the lowesty figure that you want the battery volts to drop to.


this will cause a max amps charge of 50amps until bulk voltage is reached then the current will slowly drop off and when the absorption time period ends float will take over and if thats less than the battery voltage the amps should be zero


5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

krby avatar image krby commented ·

(I accidentally put this as an answer, moving it to a comment on your answer)

Ok so:

  • charge current will be 50A, bulk stage will be the constant current phase.
  • absorb voltage should be 28V, my target "batt full" voltage. This will be the constant voltage stage.
  • Absorb time should be...as low as possible? It sounds like the Multiplus only stops absorb based on time, not based on charge current (I'd like 0.1C, so 5A in my example). Could there be an assistant to do this?
  • float voltage is 24V or something lower than absorb so it never kick in during regular charging?

One concern I have is that during the float stage as you described it is that the MultiPlus isn't fully disconnected from the battery, even though now current should be flowing. It is my understanding that for Lithium batts, you really want to leave them alone after finishing the CC phase.

0 Likes 0 ·
Show more comments
tkrull75 avatar image tkrull75 commented ·

Hi Paul/krby,

I have a very similar issue and am wondering if what you suggested was confirmed to work? I tried to push the float voltage in the multiplus-II to 48V (I have a 48V system) in order to turn it off - all that did was getting the inverter to pull as much current from the battery back into the grid in order to get down to the 48V - rest assured I quickly reverted it back to the 54V I have it set to. This means my battery still sits on float and I am not able to turn that off - are there any other suggestions?

0 Likes 0 ·