Hi
In the charging settings the VE config the highest voltage possible to be set is 64.4 volt. Is this the upper limit? I would need 65.6 volt if possible. The Quattro accepts 66 volt in the DC inputs.
Have three 15 kVa units.
Merry Christmas!
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi
In the charging settings the VE config the highest voltage possible to be set is 64.4 volt. Is this the upper limit? I would need 65.6 volt if possible. The Quattro accepts 66 volt in the DC inputs.
Have three 15 kVa units.
Merry Christmas!
As I know 64V is the limit and cant be changed.
Why you need such a high voltage?
My battery bank is 65.5 volts (16s8p). When i connected and started up everything i had 2 of the "banks" relays not connected properly and the rest of the pack was used down. In order to be able to connect the two remaining i must get them up to 65.5 volt so i avoid current rush between them. Total capacity is 185 kWh....
Additional resources still need to be added for this topic
13 People are following this question.