Phoenix VE Direct connect on Venus

Hello all,

I have install a Phoenix V.E. Direct 24/800 (firmware 1.17).
I have connect it to Venus (firmware 2.41).
From the first day until today inverter appeared on venus but loads are 0W.
Battery voltage is ok but loads are 0W.

Should i change something?

Thank you

Phoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Alexis Kalogerakis

the ve.direct inverters will not show in the AC-loads section, you need ve.bus equipment for that.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexis Kalogerakis avatar image
Alexis Kalogerakis answered ·

Hello @Daniël Boekel (Victron Energy Staff)

I thought that firmware 2.30 would be compatible with phoenix inverter v.e. direct, based on the topic below:
https://community.victronenergy.com/questions/9564/phoenix-ve-direct-connect-to-venus-or-color-contro.html