question

sieade245 avatar image
sieade245 asked

Phoenix Battery Charger Bulk Protection

Hi everyone. I've got a snag on one of our installations. There are 3 24V battery banks A200 of 12x2V cells 225Ah total capacity each bank. Each is charged using Phoenix 24/16 charger using default factory settings.

During a recent inspection, we depleted each bank to around 23.5V and then charged them back up again. Each Phoenix charger failed after between 6-7 hours. There is a solid red fail LED illuminated but nothing else.

For the main bank, we swapped in another phoenix and exactly the same problem after 6-7 hours. A skylla-TG 24/50 was then installed instead and set to 16A charge current. This failed after 10 hours with a flashing bulk, steady fail LEDs. This indicates bulk protection mode has kicked in (there is conflicting info in the manuals, one of them says it will swap straight to float, but another manual says it will fail with LED code as above).

So I'm thinking we need to increase the charging current to at least 25A for a c/10 rate. I manually set it to 40A just to get the batteries recharged and this worked fine.

My question is. Is this what is causing the Phoenix 16A chargers to fail also? I looked at the manual and also in google. There is no mention of this series having bulk protection mode. Also, if there is bulk protection mode does it default to 6-7 hours? We had exactly the same issue last year on another site, with both phoenix chargers failing after 6-7 hours but just gave up and swapped them for skyllas which have been fine. I can't believe that all our phoenix chargers are faulty though. This does not happen in float mode with already charged batteries, only after bulk mode has been on for 6-7 hours (best I can do from telemetry indications). The ambient temperature is around 10-15 degrees C and there is around 2 feet spacing around each charger. They do not get hot and the fans are working. The batteries are 2 years old. On the other site, they were 3 years old. Fitting a skylla removes the issue (at both sites).

Just to be clear. These are the Phoenix chargers, not the inverter/ multiplus units.

MPPT ControllerschargerPhoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
sieade245 avatar image
sieade245 answered ·

Hi Daniel. Yes they all will restart correctly after a power cycle. The problem is we have to physically go to the station to do this. I've done some more work on this fault since I posted the question. Each battery bank is 225Ah we have 5 banks across two sites. The station load was around 10A and they are the 16A versions of the charger resulting in a charge current of only 6A. Each charger will fail a few hours after switch on. I brought one back to the workshop and put it on the bench, connecting it to a load bank drawing 10A and a completely different battery bank in parallel which was around 50% SOC. The charger failed in the middle of the night. I'm going to connect it up to a scopemeter and log how long it is before they fail.

As the new phoenix charger-I has bulk protection which is user configurable via Bluetooth, and its clearly documented in the manual, I was guessing that the old version also has some kind of bulk protection feature but just need confirmation. We've replaced the two main chargers with Skyllas 30A which should get the bank charged back up before bulk protection kicks in.

We've reached out to our distributor but they don't know the answer, they were going to refer us to Victron support but that was 2 weeks ago now not heard anything back is there anyone I could contact at Victron directly who would know the answer to this?

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @sieade245

Can you connect the Phoenix with MK3 - usb cable to computer to check the settings?

0 Likes 0 ·
sieade245 avatar image sieade245 Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Hi Daniel. I have all the programming kit sure....but I've never used this on a Phoenix before. Multiplus/ Quattros yes. There is a port on the Phoenix but the manual only mentions using it for the external remote panel. Are you saying I can connect to it with VEconfigure? Or a different program. This is news to me, I would have tried this earlier. I'm off work for Christmas but I can try plugging a MK3 in when I get back

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

Will the MK3 work with an "old" Phoenix?
I thought you will need a MK2 for that.

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ Matthias Lange - DE ♦ commented ·

I'm not sure, what is the model and firmware number of the device?

0 Likes 0 ·
Show more comments
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @sieade245

Does the Phoenix charger start again after a power cycle?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.