What does new feature Switch "Inverter Only" actually mean on Multiplus/ Quattro? Does it mean ignor Grid or Generator? It is just opposite to Charger off ?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
What does new feature Switch "Inverter Only" actually mean on Multiplus/ Quattro? Does it mean ignor Grid or Generator? It is just opposite to Charger off ?
Yes it means Inverter ON (only)- powered by the battery.
Charger OFF
AC Passthru OFF
Effectively AC In (if present) is totally ignored.
Charger OFF
AC Passthru ON
DC Powered from battery
Hi,
I have an ESS-system with Multis+MPPT+batteries as well as AC-in-coupled microinverters.
During winter with low PV-yield, it's just perfect that the Multis also use the microinverter-power to charge the batteries.
But during summer with a lot of PV-surplus, it would be fine if (in the morning) the batteries would only be recharged by MPPTs instead of transfering the ACIN-surplus to DC.
This would save the Multis from the unnecessary tranfer-load.
I tried "Invert only", but as described in this threat, this mode seems only to supply ACOUTs, because the DC-surplus immediatly stops being transfered to ACin.
I assume my intention cannot be realized.
Bye
Alex
I have the same situation as you @schollex
I also want to load the battery only with the MPPT as there is more then enough solarpower during the day and instead I would like to see the AC-coupled Inverters to either directly supply the loads or to export the excess energy to the grid.
I did not find a solution for that yet, running a ESS System...
Maybe someone has an idea in the meanwhile...
Thanks @schollex , but this solution does not work for me. I tried this before, and tried it again just right now, but then the whole system just stops charging. MP2 as well as the MPPT. I tried some number inbetween, like 1A...5A... then the energy is (more or less) split bei 50/50 from both sources... Maybe I have some other settings or different firmware versions... Well it's not that cruial for me. ;-)
Just a suggestion. I use the Multiplus on a boat and also just want to have the Pass-through mode enabled, while the MPPT charges the battery. To do so I have added the "Two Signal BMS" assistant. like so:
I connected the Aux input of the MPII to a relay output on the Cerbo. Now I can control the charger from the Cerbo / Node red.
Not sure if this would also work for you ESS setup.
After some more thoughts to that, - I'm wondering why this should work at all?
DVCC is specially made to control the Battery current and voltage. So why it should not affect the MPPTs?
E.g. if you have multiple MPPTs, and they are able to deliver way more power then the battery can take, this is the mechanism to control the current. So why this should have no influene on the MPPTs @schollex ?
@AlexV Thanks for the hint, but this will not work in my installation.
I read about CCL not being applied within the forum - perhaps it was this post.
See the DVCC-documentation chapter 11.4.1:
6. DVCC charge current limits are not applied to DC MPPTs when ESS is enabled with Allow DC MPPT to export. This is to get maximum output from the solar panels for export.
Thanks @schollex . Now this makes sense again. I have ESS running, but DC excess AC export is not activated. That's why CCL is limiting also for my MPPT.
I will active the DC excess AC export and check again... unfortunately this needs to wait a few days as the weather is only a few amps outside today. ;-)
19 People are following this question.