Lynx Shunt VE.Can Transmit Frequency?

Is it possible to adjust the transmit frequency of the current data (PGN 0x1F214 / 125708) from the Lynx VE.Can shunt? In our system it only seems to broadcast about once every 1.5 seconds. We're trying to feed the data via CAN to an alternator regulator and there's too much latency for the control to stabilize.

More generally, is there any documentation available for the Lynx Shunt VE.Can standalone? All I can find is the manual for the Lynx Ion w/ Shunt, which seems quite a bit different.

Thanks.

VE.Canlynx shunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
jeroen avatar image
jeroen answered ·

You can send a NMEA2000 complex request 0x1ED00 to alter the timing. It is in 50ms steps, you cannot go below that. I have no idea about the documentation though.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jeroen avatar image jeroen ♦ commented ·

and for completeness, it is stored, it only needs to be done once.