question

djibi avatar image
djibi asked

Multiplus and fronius

Hello everyone, I want your help for this .

I want to use Fronius primo 3K and multiplus 800Va to avoid injection. SO my question is that the fronius primo 3K can be put on the AC out of the multiplus 800VA, for me it is impossible since the fronius output is bigger than the multiplus 800Va.


Any suggestion are welcome.

Fronius
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

You are correct. You cannot connect a PV inverter on AC-OUT which is more powerful than the MultiPlus. This is known as the factor 1.0 rule.

https://www.victronenergy.com/live/ac_coupling:start#the_10_rulemax_pv_power_must_be_equal_or_less_than_the_va_rating_of_the_multi


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

djibi avatar image djibi commented ·

Thanks.


But can i connect other inverter like Sma or Goodwe to the multiplus?

0 Likes 0 ·
Show more comments