question

ramassamy avatar image
ramassamy asked

ESS stop working in my system

Hello everyone,

here is my system:

2 MultiGrid 48-3000-70 (MASTER & SLAVE)

8x6 Battery Crown 350ah

PV inverter at AC out 2200w solar pannel /PHotowat(DANFOSS) ULX1800i

. So I use ESS ,it ran perfectly for about a month, which means I could charge and discharge the battery with energy from/to grid ,setting grid point to use the battery at night with A/C

. Until one day,nothing is working,and my Multiplus stills in Absorption and Float

Sometime the ESS reacts to the setpoint ....My SOC stills at 97% to 100% and most time, these LEDs Mains On, Absorption and Inverter are on at the same time and now the Inverter led stop lightening...

I've done:

-all firmware to the latest

-resseting


thanks for your help

https://vrm.victronenergy.com/installation/43376/dashboard

@Daniël Boekel (Victron Energy Staff)

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @ramassamy

I've found the cause:


You are using German grid code, with the option 'use aux1 to disable feed-in' selected.

Also you have a sensor connected to aux1


This sensor causes feed-in to be disabled.


Simply uncheck the 'disable feed-in' option to fix this.


I'll add this to the faq.


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ramassamy avatar image ramassamy commented ·

Hi, you are certainly right, but when i try to de-activate it, i have a message warning for a grid code... And now here is my problem, i am very far from Europe in REunion island ,and the last seller where i bought my victrons Multiplus took them from Germany . Now it is closed. Plus, i am in REUNION island a French Island

Can i have a pass word please ,can i still with the german code

@Daniël Boekel (Victron Energy Staff)

0 Likes 0 ·
ramassamy avatar image ramassamy commented ·

Excellent analyse of my problem ... Thanks Mr Boekel for your Help

Daniël Boekel (Victron Energy Staff) avatar image
@Daniël Boekel (Victron Energy Staff)
0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @ramassamy, Did you try to reset the multi? also make sure the switches are on the 'I' position and not "II'

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ramassamy avatar image
ramassamy answered ·

1)what switches are you telling??dip switch ??

2)i have not resetting the multi now...i have first do it ,but nothing happened (firm 462) and i am with firmware 465 (is RESET= ON/OFF Switch on and switch Off the multi ,if not i have not resseting )

what happen if i resset the multi by thye CGX ,do i need to re-install settings and assistant ?

@Daniël Boekel (Victron Energy Staff)



resset.jpg (39.8 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @ramassamy

1)what switches are you telling??dip switch ?? --> not the on/off/on switch at the bottom of the unit (right side)

2)i have not resetting the multi now...i have first do it ,but nothing happened (firm 462) and i am with firmware 465 (is RESET= ON/OFF Switch on and switch Off the multi ,if not i have not resseting ) --> yes, reset in CCGX is basically the same as switching the units off and on again, no settings will be erased.

what happen if i resset the multi by thye CGX ,do i need to re-install settings and assistant ?

0 Likes 0 ·
ramassamy avatar image
ramassamy answered ·

i have done the reset by the Multi GX, the problem stills...

@Daniël Boekel (Victron Energy Staff)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ramassamy avatar image
ramassamy answered ·

1)what switches are you telling??dip switch ?? --> not the on/off/on switch at the bottom of the unit (right side)


@Daniël Boekel (Victron Energy Staff)

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

No, the on/off/on switch at the bottom of the unit (right side)


Please read Q9 of this faq:

https://www.victronenergy.com/live/ess:design-installation-manual#faq


0 Likes 0 ·
Show more comments
ramassamy avatar image
ramassamy answered ·

Hi

you found exactly my problem ... Thank you for all...ESS is working perfectly now!!

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

aes avatar image
aes answered ·

Hi, I have the same problem but I can not read the solution you have found. How can I solve this problem?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.