How can I reset the VE.Bus or what else can I do to work make the CCGX/inverter work with DVCC and the BMS of the batteries?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
How can I reset the VE.Bus or what else can I do to work make the CCGX/inverter work with DVCC and the BMS of the batteries?
What assistant are you running, and what are your settings?
THX J
Your inverter in the Easysolar 48/3000/35 has firmware that is too old (v413)
You need a version above v422:
https://www.victronenergy.com/live/ccgx:start#dvcc_requirements
Ok great! But so far there is no higher firmaware available on the regular way.... unless I go to professional.victronenergy.com. and do it manualy... right? I have the MK3/USB interface but since I am enduser is in my case any risk in updating?
THX Jean
If you are not comfortable doing this, please get an experienced user / installer involved.
updating instructions can be found here:
https://www.victronenergy.com/live/updating_firmware:updating_ve.bus_products
THX Jean