2 x Multiplus split phase setup with ESS

We're looking at adding solar and a battery backup for our house in the US and I was hoping to get some feedback on the setup I'm planning before purchasing the equipment to make sure it would work. Any feedback would be appreciated, thanks in advance.


Multiplus-II
victron-ess.jpg (91.1 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gharris avatar image gharris commented ·

Did you end up using 2 multiplus with split phase? Was it problematic like mentioned above?

0 Likes 0 ·
4 Answers
ee21 avatar image
ee21 answered ·

I don't want to step on anyone's toes who have already given their feedback, however I started using Victron equipment with 0 prior experience about 2 years ago now. I started with a single Compact Multiplus 2000, and some DIY batteries. I love that you can scale up their equipment, and to date, have thus far scaled up my system to a combined split-phase+parallel system with a total of 4 CMP 2000's (2 in parallel on each phase) for a combined output of up to 6400 watts...


I was very intimidated when first attempting a split-phase setup, using just two CMP 2000's about a year back now, however with just a couple online videos, I was able to navigate though VEconfig pretty darn easily and setup the both in a 180* split which is what we use here in the US.


The biggest issue with these "complex" setups is getting the wiring right, as you really are supposed to have identical lengths and sizes going from the battery to each inverter/charger. All this really means is, if one of your two inverter/chargers is a little further away from the battery, the other one will need to be left with a little additional slack so the runs are the same length. I don't feel like this is rocket science to get done right.. You just need a tape measure.


Split-Phase+Parallel gets a bit more complicated beyond this, as you then need to match the AC wiring side. If you are using only 1 inverter/charger per phase, this is not needed.


Apart from the wiring itself, yes, technically there is the potential for overload on one phase.. But so is there with your connection coming from the grid.. If you are not familiar with how split-phase 180* electric works, the principal is rather simple:

Say you have 100A 240V service coming from the grid - by definition, this should allow you 24,000 watts of loads. However, this gives you 100A 120V on one phase angle, and 100A 120V on the other phase angle. It is possible, if your house was wired poorly, for all your 120V loads to end up on 1 phase angle. If this were to happen, the main breaker of your house would trip if you used more than 12,000 watts at any one given time.


The way it works with a split-phase Victron system is identical, but on a smaller scale. I have 4x CMP 2000's with a continuous load rating of 1600w, which should give me 6400w total technically. But since this is split up between two phases, the maximum 120V power I could draw, from a single electric circuit, would only be 3200 watts. What I can do instead however, is draw 3200 watts 120V from the outlets in my kitchen, 3200 watts from the outlets upstairs since those two circuits are each on different phases. Or I could take 1600 watts from the kitchen, 1600 watts upstairs, and 3200 watts 240V from my EV charger, all at the same time.


All this means is your electrician with have to do their best to balance any 120V circuits you are connecting across the two phases available.. Again, not rocket science, it's pretty simple math/common sense. The issues with something like this tend to come from having something like 6 120V circuits, on a small system. Even if they are split up 3-and-3 on the two phases, you might be running a 1800 watt heater on 1 circuit, and a 1800 watt vacuum cleaner on another circuit. If those two just to happen to both be on the same phase, your system (in my case at least with 3200w max per phase) would overload and shutdown. This would be even though I'm only using 3600 watts, on what is technically a 6400 watt system.


My advice here - either oversize your inverter/chargers, buy more VA's than you think you need... OR, just be mindful not to run any extremely large 120V loads if the grid fails.. I use a little home-automation to make sure no 120v heaters or anything are running if the grid goes down.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

solardude avatar image
solardude answered ·

If you have any specific questions you will get better results. Everyone here is happy to help, but you’ll have to be more specific in what you are looking for.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Eli Hunter avatar image
Eli Hunter answered ·

Thanks for the response.

I've spoken with two dealers this past week who both tried to push me away from split phase due to complexity and the electrician I'm working with has kind of pushed backed on splitting the 240V equipment off to a separate sub panel.

I've tried to research as much as I could and don't see why this won't work, just wanted to make sure before I take the plunge. Guess I'm just looking for some reassurance that this will work.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

solardude avatar image solardude commented ·

They are not wrong, split phase can get complex. If you don’t HAVE to have 240V appliances on battery backup, 120V systems are much simpler and less expensive. Not trying to talk you out of it, just want you to be aware it requires a lot more planning and wiring.

No matter what, you need to have an inverter bypass installed. Without it, if any component goes down, you lose power to ALL of those circuits until its fixed.

That having been said, I have an offgrid split phase system that works perfectly. Glad I did it, but it’s definitely more complex than 120V.

0 Likes 0 ·
vincent avatar image
vincent answered ·

I've done a bunch of split phase systems like this, and they definitely can be more problematic. If anything goes wrong on the ve connection, both shut off. They are quick to overload on one phase and shut off. Basically you're multiplying your risk of issues.

I've had much better experiences since I've started listening to Victron's advice and using autotransformers on the output for split phase. I recommend you do the same.

Ditch the two multiplus and buy a big 230V model (they adjust to 240/60hz). Next up your DC system voltage, it will save you a ton on copper, and it just works better, much less heat and i2r loss. I recommend 48V.

Input 240V only, no neutral, and then output to an autotransformer for your 120/240 subpanel.

2 |3000