question

Sten avatar image
Sten asked

Why can’t I use Battery Protect with reverse current?

Hi

I wonder why I can't charge through BP from output to input.

As I understand mosfet can cary the same current reverse as forward.

I do understand the problem with uncontroled reverse current but if the reverse current is controled by a solar charger that can't output more than the BP rating, whats then the problem.


In the BP manual the warning is only for use in battery to battery charging where the current can't be predikted.


"Caution: uncontrolled reverse current will flow through a Smart BatteryProtect if Vout > Vin. Therefore, never use a Smart BatteryProtect for

battery to battery charging."


Thanks.

Battery Protect
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

The battery protect limitation applies to reverse currents, whether they are from controlled or uncontrolled sources.

Please check this site for the most recently up to date manual for your product, as this was recently clarified:

https://www.victronenergy.com/support-and-downloads/manuals

I may be wrong about the reasons and am happy to be corrected. I think it’s because when the MOSFETS are off, the resistance increases, but the reverse currents are not blocked. The extra heat generated is greater that the dissipation potential of the heat sink, which is designed for the normal very low resistance dissipation situation.

There is some more discussion about it here: https://www.edaboard.com/showthread.php?258134-Do-MOSFETs-conduct-in-both-directions

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Sten avatar image Sten commented ·

It could be the reason, but try reading page 21 in this document about reverse current in mosfet.

Infineon OptiMOS Power MOSFET Datasheet Explanation - Infineon Technologies


Sorry if this get technical.

0 Likes 0 ·
Show more comments
randyp avatar image randyp commented ·

Thank you for the link to the New BP, SBP manuals. Reverse current operation is excluded from BP designed usage. Wish I had known this when I bought and used a BP-100 to control battery charging over voltage. Luckily, the BP did not smoke, but it might be damaged, through no fault of my own.

Cannot find an explanation of the d mode of the BP / SBP. Wonder what it is used for ?

0 Likes 0 ·
Show more comments
Tom avatar image
Tom answered ·

There are other electonic non Victron devices (switches) on the market that do what you are looking for, but unfortunately they cost $600. The BP65,100,220 just is not designed for your needs. Also a basic $40 Kilavac contactor with a precharge $2 resistor plus a $10 Chinise programable under voltage PCB will function for your needs (i am assuming not knowing your complete specs).

I removed my bp220 between my battery and multiplus and replaced with the contactor and pcb used as a switch and a third safety low voltage shut down. My BMS is my primary individual cell monitoring device and the Multiplus and mppt settings as the secondary safety.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.