question

valentin-silvera avatar image
valentin-silvera asked

BMV and internal Multi battery monitor

Hello everyone. I have a system composed of the following elements:

1 Venus GX (Firmware 2.33)

1 Multiplus II 48/3000/35-32 (Firmware 456)

1 BMV-712 Smart (Firmware 4.03)

1 Smart Solar Charger MPPT 100/20 48V (Firmware 1.46)

4 Battery 105Ah in series, 48V


The battery is being monitored by the BMV:

Settings → System setup → Battery monitor → BMV-712.


I have two operation problems:

1) During discharge without grid (off-grid), with a C4 rate, it did not respect the configuration of the cut-off value of the state of charge that was SOC = 50% in the BMV. In repeated tests the cut-off voltage value was around 47.40V.

2) During recharge, the process does not respect the values set in the VEconfig3,

As shown in the image below:

The bulk stage was started with SOC = 95% instead of 80% and the load current was 5A instead of 10A.


In the following link: https://www.victronenergy.com/live/ccgx:start#battery_state_of_charge_soc say

“Note that the Battery Monitor setting in VEConfigure3 is irrelevant. For systems like this, changing this setting will have no effect on the charge - or any other parameters - in this type of system.”


In this case, when using the BMV, how can I configure the parameters for the loading stages?

battery chargingBMV Battery Monitor
1574978608486.png (33.1 KiB)
1574978684221.png (99.1 KiB)
1574978692931.png (80.8 KiB)
1574978755322.png (51.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

You maybe getting confused as the Battery monitor in the Inverter is NOT the BMV712

(I would turn off that battery monitor in the inverter and only work on the BMV 712 figures)

you should use the victron connect app and setup the BMV 712 if you have not allready done so as the battery size setting may not be correct in the BMV


The System starts in Bulk and then changes to absorption when the set voltage is reached

Also check that the CCGX has the correct Battery monitor selected it should be the BMV712


The VRM screen shots are from the BMV

the screen shot of the inverters internal bat monitor i a different VRM graph

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Please do not turn off battery monitor in the Multi.

If it is enabled, and a BMV is chosen as battery monitor in the GX device, the Multi's SOC values will be overwritten by that of the BMV

0 Likes 0 ·
Show more comments
PeterM avatar image
PeterM answered ·

What is the correct answer as two conflicting solutions are presented - One solution - have both Battery Monitor in inverter and BMV enabled and the other solution disable the inverter's own battery monitor

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Victron BMV battery monitors product page

Additional resources still need to be added for this topic