tbird asked

Low voltage but Shunt reading high charge.

Hi there people,

So I’ve been away for a few weeks and my friend has been staying in my place.

I have a Smart Shunt, a 24/800 inverter and a 100/50 MPPT.

2 x 230ah 12v lead acid batteries wired to 24v.

Despite having a discharge floor of 60% - which hasn’t been reached - the 24v batteries have been as low as 18v which tells me they are wrecked.

I woke up this morning and I’ve got a low voltage alarm and no power despite supposedly having 82% in the tank.


I don’t understand how the deepest discharge can be 77ah and take the voltage down to 18.56. Calibration error?


Any ideas what I’m doing wrong?

How can the voltage get so low without hitting a charge cycle / the discharge floor?


Many thanks…

886c713a-c7ca-4c33-9641-8983c33e4621.png

298fe6c5-0b1a-4d0d-b9a9-6242f5986221.png


battery system voltagelow battery warningdischarge level
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
pwfarnell avatar image
pwfarnell answered ·

Show us your SmartShunt settings, you may have it set wrong so it resets to 100% charged before it is actually fully charged. Also, batteries lead acid or lithium and what the is your absorption voltage set at.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tbird avatar image tbird commented ·

Many thanks for your reply…

I’ve got lead acid batteries…

I just reset the settings to default, but I think absorption was over 29v and equalisation was 33v.

677cea90-6b10-4ecb-9c12-738bdd6b2102.png

130ff48c-d665-45aa-ac8f-b04916b0ecb2.png

0 Likes 0 ·
chrigu avatar image
chrigu answered ·

Your charged voltage is at 24.0V, so anytime the battery goes over 24.0V and the charge current goes below 4% for 3min, the shunt resets the SOC to 100%


Set it to 27.4V, float voltage -0.2V

https://www.victronenergy.com/media/pg/Lynx_Shunt_VE.Can/en/battery-monitor-settings.html

And although the discharge floor is at 69%, i assume theres nothing actually stopping a discharge. Personally i would have set battery capacity to 115Ah, so the SOC will say 0% but actually its only 50%, but you cant really ask more of lead acid. Just a psychological thing, seeing 0% is more meaningful than seeing 50%

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tbird avatar image tbird commented ·
Much appreciated.


I’ve changed the settings although for these batteries I’m sure it’s already too late. I’m getting voltages of 30v…. I’m assuming that’s because they’re damaged?


And yeah, there’s nothing stopping a discharge from happening. In my little head the shunt would prevent the batteries getting damaged but I suppose I need another bit of kit to prevent draw on the system when the voltage gets too low…


Thanks again for your answer and the link

0 Likes 0 ·
Show more comments
pwfarnell avatar image pwfarnell commented ·
@TBird If the main charge is by solar it is better to set the SmartShunt charged voltage to 0.2V below absorption voltage i.e. 28.6V not the float voltage. This is because if you use float voltage then shading on your panels can reduce solar power so your charging voltage and current falls and the SmartShunt takes this as charged.

@Chrigu

0 Likes 0 ·
Show more comments