Lynx Shunt and fuse type?

Hi,

My Victron supplier who sold me the Lynx shunt doesn't have a 400A CNN fuse.
Is it ok to use an ANL fuse of 400A instead of the CNN?

My system has external fuses and if there is nothing else involved for the fuse on the shunt then to blow when overcurrent is flowing between battery and units then i in reality could just connect a piece of copper.

Kind Regards

lynx shunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
kai avatar image
kai answered ·

One of the key things in battery systems is to ensure you have a suitable fuse located as close to the battery as possible. It guards against the possibility of an electrical short downstream of the battery that ultimately starts a fire.

As to the rating of this battery near the battery - If you are using a SLA bank then I'd suggest that the ANL substitution is ok. If you are using a lithium chemistry then I would suggest an external fuse rated for the potential short circuit currrent would be preferred over both CNN and ANL types.

See also

https://www.victronenergy.com/live/dc_distribution


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ehsab avatar image ehsab commented ·

Hi Kai, and thanks for your post.

I will place an external 400A batery fuse before the Lynx shunt (before it even reaches the Lynx Power In), so i don't really need a fuse inside the lynx, but i need to bridge the postitive ends inside since there now is a gap :)

And my Victron dealer has an ANL fuse of 400A.

My battery is a 380Ah Lead bank.

0 Likes 0 ·
Show more comments
meltemicaz avatar image
meltemicaz answered ·

I would like to understand why the "lynx 1000" system is listed in the marketing literature as a 1000 amp system does not have a 1000 amp fuse for the lynx Shunt? The largest that I can find is an 800 amp CNN fuse from Littelfuse. The specs in on the Victron website indicate that the shunt can handle 1000 amps continuous. What am I missing here?


230-588-20180706090107.png

screenshot-2023-01-25-at-084911.png


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kienan avatar image
Kienan answered ·

I found a fuse that I believe will work great. It is rated for 1,000 A, 100Vdc, 100 kA interupt rating (much better than CNN). These fuses are kind of expensive, but they will allow you to use the Lynx shunt to it's full potential.

Also, if the total sum of the fuses on either the left or the right side of the shunt total up to 1000A or less, then you don't need the main fuse in the shunt. In such case, you could use a copper buss bar instead.

These fuses seem to be backordered everywhere, but I'm bringing them into stock along with custom 1000A rated Copper bars (for when you don't need the fuse). They should all be in my stock within a few weeks and I'll post some pictures when they arrive.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lyric avatar image
lyric answered ·

I found that some of Littlefuse LT17 telecommunication fuses will fit inside the Lynx shunt. The attached is 800A with 100kA interrupt. It appears that with a little modification Victron could get a class t to fit inside their Lynx shunt case.

img-20231209-081906.jpg