Multiplus-II 8000VA 48V, number of Pylontech batteries?

I found the link below but I see this is already an old link as the 8000VA, 10.000VA and 15.000VA models are not listed:

https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom

How much Pylontech 48V/2.4 kWh can I best use for this inverter please?

Multiplus-IIPylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Alexandra avatar image
Alexandra answered ·

@Malakas

It is VA divided by the battery nominal voltage then divide that by the nominal discharge current.

The US2000 datsheet says it can do 25A continuous.

8kVa maths

Or the same as a quattro 8kva requirements

8000 ÷ 48v = 166A ÷ 25A = 6.6666 or 7 US2000


10kVa maths

10000 is easy it is 2 x a 5kVa or the dame as the quattro minimum requirements.

10000 ÷ 48v ÷25A is 8.333 batteries.


15kVa maths

15000 is also easy it is 3 x what a 5kVa system needs. Or the same as a quattro 15kva requirements.

15000 ÷ 48v ÷25A is 12.5 batteries. Or 13 US2000 since you cant have a half battery.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

malakas avatar image
malakas answered ·

Thank you very much for the clear explanation.

Ps, I was never good at maths....

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

malakas avatar image
malakas answered ·

One small question,

If we were to opt for a 5000VA (we have no idea whether this is going to be sufficient for our off-grid system). We end up with 5000 ÷ 48v ÷ 25A = 4.16666.

I suppose it would then be better to install 5 batteries (12kWh) rather than 4?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daza avatar image
daza answered ·

More batteries have got to be better in an off grid situation, but you also have to have the ability to fully charge them so that you can balance the battery cells.