I am considering adding a MultiPlus in parallel with my existing grid tie PV system. My installation is in the UK where the cables from the electricity company meter go first to two Henley Blocks for live and neutral. One set of tails from the Henley Blocks go to the house consumer unit and another set of tails from the Henley Blocks go to the solar consumer unit and from there to the PV system via the Solar Generation Meter. This is a fairly normal UK arrangement.
Since the house loads are on the AC-In side of the MultiPlus, for an ESS system I believe I need a Victron Energy Meter connected to the CCGX. If I use an ET112 in my installation I think the ET112 would need to be installed between the Henley Blocks and the electricity meter together with an isolation switch in order to measure net flow to/from the grid? But it also looks like I could use an ET340 in its dual function arrangement. The example wiring for this looks like I don't need to have new cabling between the Henley Blocks and the electricity meter. However I don't understand how this dual function arrangement can calculate the net grid flow since it doesn't measure the house loads? For example, let's say the house consumer unit loads are 2KW and the solar PV is generating 1KW so 1KW is pulled from the grid. With the ET340 in dual function arrangement, how is the MultiPlus instructed to supply 1KW from the storage battery (if there is enough energy in the battery) to end up with a net zero watts from the grid? I would very much appreciate an explanation for my example as I am currently missing something somewhere!
Hope the above makes some sense!
Many thanks,
Andrew