We have very low quality utility power with over 100 brownouts and brief power outages a day (Costa Rica). The engineer we hired was instructed to build an active UPS system with line conditioning. He just completed an install of MultiPlus IIs and a battery bank. We immediately realized the power outages are gone but our surge protectors and the small UPS units are still clicking and beeping in response to the poor utility service. I am not an electrician but know enough now that I’ve seen the install and operators manual I know enough to see we received a passive (parallel) installation. Great for covering our brief (minutes) outages, but doing nothing to protect our electrinic devices. Can anyone here provide guidance on what can be done or be added to stabilize our utility service short of a complete system replacement?
voltageac
Trevor Bird avatar image
Trevor Bird answered ·
@donlstewart the multiplus 2 monitors the input for lower voltage and high voltage surges and will disconnect from mains in either case. For a 240volt system commonly the low voltage may be as low as 180 volts before disconnecting and as high as 270volts before disconnecting. These levels can be adjusted if that range is too wide and you would prefer tighter limits.
When the variation is too great and the disconnection does take place the unit switches to inverter mode and still supply power so you will not see any change to the power supply.
I think in most cases the provision of the Multiplus will provide the conditioning you require.
lifeingalicia avatar image
lifeingalicia answered ·
you may want to watch this video about grid settings
https://www.bluepower.pro/victron-veconfig-grid-settings-tab-tutorial/
Setting the limits to a more "sharp" reaction will engage it more often but still you have the 20ms
sharpener avatar image
sharpener answered ·
You mention you have surge protectors already. It might be worth fitting these upstream of the Multis to protect them as well. If they are on the downstream side they will not provide any protection for the Multis when they have disconnected from the grid and are in inverter mode, there is still some separate circuitry connected and active in order to monitor the grid condition.
dennibu avatar image
dennibu answered ·
Ich denke, solange es parallel läuft, wird man diese kurzen Spannungsspitzen nicht verhindern können. Um das Problem ganz zu vermeiden, würde es helfen, die Akkus vom Netz zu laden und die Multis nur am Akku zu betreiben. Eventuell könnte man dann nur bei Überlastung das Netz dazuschalten.
grfloater avatar image
grfloater answered ·
Maybe your solution from start should have been an "Online UPS", like https://www.apc.com/us/en/product-range/61918-smartups-online/#products - instead of what you call "parallel" with Multi (which is more like "line interactive" UPS).
If you have PV panels, you can charge the battery and then go "island" (disconnect AC in), if inverter power is enough (given temperature sloping, as well). Without panels, only from mains grid AC, you may restrict the limits for charging / inverting, as others proposed. Or/and you may put some automation, for connecting the AC in, such as a smart switch kicking in at night, or when battery is below SOC (you can use the Multi aux relay).
Alexandra avatar image
Alexandra answered ·
@donlstewart
Other than tightening grid accepted parameters and switching on ups....
For this a solution could be to have one inverter connected to the grid for charging nothing connected to AC out. And a second one inverting only to loads (no ac input), so isolated from grid, that way you always have good voltage a sine wave on the loads but have the use of grid for battery maintenance.
donlstewart answered ·
The engineer that did the design surprised me. He truly failed to understand how bad the utility power was and thought he was doing the right thing. They are returning and converting what we have to active by bringing the utility service in to a bank of battery chargers (AC to DC inversion). The MultiPlus units will then continuously provide conditioned power (DC to AC inversion) to our home from the battery bank. That leaves the chargers taking a beating from voltage drops and outages, but they are less sensitive to wear and tear then the MultiPlus inverters, there are 4 of them, and they are not expensive to replace.