question

zwitter avatar image
zwitter asked

Multiplus wont invert.

I have a Multiplus 5000/24/120. 2x MPPT, BMV700, 400Ah Lipo4, CCGX.

the system has been working in ESS for several years no problem. Then about 8 weeks ago one night the house went black. I found the 25A breaker rhat feeds the Multi grid power tripped. I reset it and it stayed set but no power to the house. Since then the inverter just wont start.

I took the Multiplus to a victron certified repairer and they said nothing wrong.

I reinstalled and found batteries were out of balance so reballanced, installed a new BMS and still the inverter wont invert.

I have reloaded the config but made no difference.


I have run out of ideas. It should work but wont.

the multiplus just stays in bypass. I called an electrician who said he was an expert and he told me the inverter output was dead short!

any ideas, suggestions?

thank you in advance.


james

multiplus ve.bus
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

@Zwitter I called an electrician who said he was an expert and he told me the inverter output was dead short!

The output of the multi will appear as a dead short if measured with a multimeter. The output is connected to the transformer after all.

You might want to look a bit deeper.

0 Likes 0 ·
3 Answers
derrick thomas avatar image
derrick thomas answered ·

I would start by isolating the inverter from the ac in and out. Will it go into invert mode with the ac in/out isolated? If so then connect the ac out put and test, then the ac input and test. One step at a time, you need to isolate the problem.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

zwitter avatar image zwitter commented ·
Ok I have done this and posted the findings. Now what?
0 Likes 0 ·
zwitter avatar image
zwitter answered ·

Ok,

I went and did some more testing.

the Multiplus goes into invert mode when the AC in is switched off. It then appears to be happy until the battery runs out.

when the AC is turned back on it drops out of inverting in about 15 seconds.

the system is designed to be an ESS. So the batteries are just to spread the solar power into the night each day. It saves a lot of power bills this way.

so where do I goto now?

I did take the Multiplus to a certified repair centre and they said nothing wrong with it. I doubt they did or even can test the logic part of the unit.

so I need some suggestions as to where to take it for a better repair or what I can do to take this further?

I did reload the setup from backup but no change.

thanks James

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejrossouw avatar image ejrossouw commented ·

@Zwitter This will take time and patience to investigate and will be a challenge via a forum. I suggest also changing the breaker, check the internal fuse of the inverter and look at the VRM records to try and understand why it happened. Check the error VRM log for sync or ground relay errors. Check the grid code settings and measure input / output voltages to ensure they are within the required limits as others also suggested. I wonder whether the ESS not longer can see the required input energy meter data it requires to allow inverting and stops as when contact is lost with an external energy meter. You can maybe test this borrowing an external current sensor from the service centre. Lots to investigate and think about. Good luck.

0 Likes 0 ·
zwitter avatar image zwitter ejrossouw commented ·
All breakers check out ok.

I don’t know about internal fuse but the inverter detects AC in fine and the output works too.

VRM just shows the system turns off. No actual errors recorded.

grid codes are fine. We actually have an external box that verifies the voltage and frequency settings are good.

the power meter is connected and working ok.

I suspect it is a logic error around the Virtual Switch?

who are the experts in Australia able to fix this?

0 Likes 0 ·
ejrossouw avatar image ejrossouw zwitter commented ·

Have a look here and also maybe reset the inverter, reinstall the firmware and reinstall the ess assistant.

0 Likes 0 ·
Show more comments
Rob Fijn avatar image
Rob Fijn answered ·

Maybe try one more test.
Disconnect all wires of the AC output of the MultiPlus ( line and Neutral)
Switch ON and the unit will invert, right ?
Then switch ON the AC_in... does the unit now keep inverting correctly ?

If yes, then you have a loop connection at the AC-out to the AC-in, somewhere in your electrical installation.

Let us know how this goes.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic