Generator overload warning when attempting to charge batteries

Hi,
I wonder if someone might be able to help.

Our system is set up so that any excess power is exported to the grid. It has been designed so that the grid may be disconnected via a switch and batteries charged via our Generator (GT4000ESi GT Power 4000W). However, when we attempt this our generator registers an overload warning and the batteries are not being charged.
Any assistance greatly appreciated.

Thanks,

Kev

Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
JohnC avatar image
JohnC answered ·

@wombles

This is normally handled by setting an Amp limit on ACIN. There's several ways to fo this depending on the kit and the comms you're using. But you haven't told us any of that..

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wombles avatar image
wombles answered ·

Hi @JohnC
From the device list I can see that the system has:

  1. Cerbo GX Gateway
  2. VE Bus (MultiPlus-II 48/5000/70-48)
  3. Battery Monitor (BSL Bat)
  4. Solar Charger (BlueSolar Charger MPPT 150/45)
  5. PV Inverter (Fimer GT)

Many thanks,

Kev

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

The generator overload may be caused by the inverter/charger attempting to feed power into it.

When you change from grid to generator, you also need to disable grid feed-in. There has been some debate here if switching the AC input type to generator is sufficient but that would be logical. If not, you need to adjust the grid power feed-in to zero or adjust for a small amount of power drawn from the AC source.

I have incorporated support for an external transfer switch into GuiMods that may help in your system. This sets the AC input type to generator and back to grid, AC input current limit and a few other parameters. A digital input is used to tell the GX device which source is the current input.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wombles avatar image
wombles answered ·

Thank you @Kevin Windrem.
Yes, I think that is what is happening. When switching to the generator this disables the grid i.e. I have a manual cut-out switch for the grid input.
Could I ask where the AC Input Type may be found please?

Also, where can I find GuiMods?
Apologies for the questions, but as you may have gathered, I am still on a learning curve with this.

Thanks again,
Kev

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image Kevin Windrem commented ·

For a Multi, you set the AC input type in this menu: Settings / System setup / AC input 1. For a Quattro which has two AC inputs, you also need to set AC input 2 if it is used.


GuiMods is my third party package that modifies the GUI and adds other functionality like the external transfer switch support:

https://github.com/kwindrem/GuiMods

This package uses SetupHelper:

https://github.com/kwindrem/SetupHelper

The latter has a "blind install" mechanism and after that is installed you can install GuiMods from it's PackageManager menus.

0 Likes 0 ·
wombles avatar image wombles Kevin Windrem commented ·

Thank you so much Kevin.
I can see that the AC input 1 is set to Grid and AC input 2 is not set at all. So, if I set AC Input 2 to "Generator", would that do the trick do you think or is there anything else I should be considering?
Cheers,

kev

0 Likes 0 ·
Show more comments
wombles avatar image
wombles answered ·

Thank you Kevin.
I'll give that a whirl right away.
Have a great weekend.
Kev

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.